Alexandru,
The short answer is no, the circuit would not provide the equivalent of
reinforced insulation. However, have a look at 2.2.4  (60950-2000)-
Connection of SELV circuits to other circuits. You can connect SELV
circuits to other circuits provided, that under single fault conditions
(i.e. the transzorb, or fuse shorted out) you do not exceed the SELV
limits, and you have a minimum of basic insulation between SELV circuits
and the primary circuit (including the neutral).

Regards

Doug


                                                                              
                                              
                    Alexandru Guidea                                          
                                              
                    <[email protected]>             To:    
"'[email protected]'" <[email protected]>       
                    Sent by:                     cc:                          
                                              
                    owner-emc-pstc@majordom      Subject:     reinforced
insulation - EN60950                                
                    o.ieee.org                                                
                                              
                                                                              
                                              
                                                                              
                                              
                    05/06/03 12:46 PM                                         
                                              
                    Please respond to                                         
                                              
                    Alexandru Guidea                                          
                                              
                                                                              
                                              
                                                                              
                                              





Dear colleagues,

As part of a PCB design required to be compliant with EN60950, we want to
use the configuration described below, to be able to relax the traces
separation. The circuit intended to become SELV is accessible to the
operator.

Questions:
1. Is the combination of Basic Insulation + Fuse&Transorb(15V) equivalent
to
Reinforced Insulation?
2. Does the transorb have to comply with a specific EN safety standard
(like
one applicable to Y caps)?

Thanks,

Alexandru Guidea

CAE Inc.
Canada





            Basic
         Insulation
                |
                |
ELV--------||-------FUSE--------------SELV (??)
                |                      T
                |                      R
                                       A
                                       N
                                       S
                                       O
                                       R
                                       B
                                        |
                                        |
                              GND (EARTH)





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to