> Dear all,
> According to Section 4.1.3 Voltage probes of ANSI C63.4, "A voltage probe
> may be used for radio-noise voltage measurements when measurements are
> made at a user's installation (see 5.6) or when the ac current level
> exceeds the current-carrying capability of commercially available LISNs.
> For such measurements, the method shown on Figure 4 may be used. Special
> precautions shall be taken to establish a reference ground for the
> measurements."
> Accord to Section 5.6 Testing at manufacturer's location or user's
> installation, "The voltage probe (see 4.1.3) shall be used for ac
> powerline conducted emission measurements. (See IEEE Std 13-1988 for
> additional information.) Neither a reference groundplane nor an LISN shall
> be installed for user's installation testing unless one or both are to be
> a permanent part of the installation."
> The above sections seem to me to contradict one another regarding the
> reference groundplane.
> Can we interpret the above (Section 4.1.3 "Special precautions shall be
> taken to establish a reference ground for the measurements.") to be
> applicable only when testing in the laboratory and the ac current level
> exceeds the current-carrying capability of commercially available LISNs?
> Please comment.
> Thank you in advance
> David Shidlowsky
> Technical Writer
> EMC Laboratory
> ITL (Product Testing) Ltd.
> Kfar Bin Nun
> Israel
> Tel: +972-8-9797799
> Fax: +972-8-9797702
> Email: [email protected]
> http://www.itl.co.il
> http://www.i-spec.com
> This e-mail message may contain privileged or confidential information. If
> you are not the intended recipient, you may not disclose, use,
> disseminate, distribute, copy or rely upon this message or attachment in
> any way. If you received this e-mail message in error, please return by
> forwarding the message and its attachments to the sender.
> 
> 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to