Doug,

I have used fuses of 5X the nameplate current in both UL and CE marked
products. The fuses were normal blow and were there to protect against
single-component failures, not against the input current somehow slightly
exceeding the name plate.

   Dave Cuthbert
   Micron Technology


From: [email protected]
[mailto:[email protected]]On Behalf Of POWELL, DOUG
Sent: Friday, December 12, 2003 11:16 AM
To: EMC-PSTC (EMC-PSTC)
Subject: Fuse Ratings for thermal considerations



Hello all,

Generally speaking, in the US, one may not use a fuse value of more than
125% of the rated current of a product.  However, when I look at the
application guides for fuses, they are thermally derated on a curve.  One
fuse type drops to 75% of its marked value when used in an 80C ambient.
Another is not so severe, but none have a flat curve.  This is to be
expected as fuses are designed to open with RMS heating.

Here is a scenario that describes my problem:

If the product has a MEASURED input current of 0.8 amps and is subsequently
RATED for 0.8 amps, then theoretically, I allowed to use a maximum fuse
value of 1 amp.  If I select a 1 amp fuse and use it in an elevated ambient
environment of 80C, it is going to reliably open at 0.75 amps, and I will
experience nuisance tripping.  The engineering side of me says I should use
the manufacturer's derating curves and reselect a fuse at a higher value.
The equation to select the fuse would be 1.25*(Rated Current)/(Fuse
Derating).  The answer is 1.33 amps and I would probably select a 1.25 amp
fuse.  This is 156% of the product rating!

My problem is, I've already had one agency tell me I can't do this.  Has
anyone had experience on how to solve this problem?

Thanks, -doug




Douglas E. Powell 
Corporate Compliance Dept.
Advanced Energy Industries, Inc. 
Fort Collins, CO 80525 USA 


_______________________________________________________________
This message, including any attachments, may contain information
that is confidential and proprietary information of Advanced 
Energy Industries, Inc.  The dissemination, distribution, use 
or copying of this message or any of its attachments is 
strictly prohibited without the express written consent of 
Advanced Energy Industries, Inc.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to