Robert -

Please refer to the below.  It is assumed you meant to
reference CSA/UL60950 for power cross requirements, rather
than IEC 60950.  It is also assumed you meant Figure 6C,
rather than Figure 5C.

The below is somewhat stream of consciousness; please
forgive the format of the response.

> From: Robert Johnson
> Sent: Wednesday, November 26, 2003 7:27 AM
>
> When using coaxial cable for TNV-1 purposes, I
> have trouble figuring out how to apply clause 6.
> A typical example is “fiber to the curb” where
> the final service drop from the pole to the subscriber
> is made with small coax such as T3 lines.

I'll assume T3 is a purely figurative example.  The bulk of
fiber-to-the-curb I've seen (it has been a little while)
were intended to provide POTS, Ethernet, CATV type
(movies-on-demand), broadband and similar services, mostly
to small businesses and residential subscribers.  T1, T3,
etc., might be offered now, but weren't among the services
contemplated when Mr. Peabody took his boy Sherman through
the Wayback Machine.

> The cable shield is grounded at the equipment
> 6.1 can be passed by having the serviceman ground the
> equipment (6.1.2.2).

Per US NEC, Article 800.33, the cable shield must also be
grounded, as close as practicable to the point of entrance
to a building.  See also CEC, Rule 60-306.

> 6.2 can be passed by grounding both TNV and SELV.

And the grounding meets the requirements of §2.6.

> 6.3 is passed since no power is applied to the
> TNV circuit.

Yes.

> 6.4 is a problem however since primary and secondary
> protectors are not used.

Do you intend to mean primary protection in the equipment or
at the building entrance?  It is not very common, but
sometimes so, that primary protection is incorporated into
equipment.  The assumption of the standard is that primary
protection is present, based on Code requirements (NEC
800.12 and CEC Rule 60-200).

Secondary protectors are not required by the Codes or the
standard.  The requirements for secondary protectors are
related to the 100 A²·s current limiting and 1.3 A
overcurrent protection requirements in the left hand column
of Figure 6C; not as a "requirement," but "considered to
meet" the requirement.

> The central path of figure 5C can be used for
> compliance since the coax is greater than 26 AWG,
> the circuit is grounded, and an enclosure and
> spacings are provided.

Here is where divergence from 100 A²·s current limiting
occurs, moving to the middle path of Figure 6C...

> However, this does not solve the problem of a power cross
> where up to 25 amps (-or more; I believe this figure came
> from the twp lines) may be carried into the building to
> the equipment on the coax, overheating the telecom cable.

Here is where divergence from the middle path occurs.  One
must assume the product does not provide the 120V isolation
anticipated by Note 4.  Either §6.1.2 and Figure 6A testing,
or a simple EST demonstrates compliance and the middle path
still applies...

§6.1.2 assumes overvoltage protection exists in the
equipment, but if it does not, an EST meets the middle path
requirement.  You say spacings are met, so this would be
easy...

If you have to go through Test 5, you will need some form of
overcurrent protection, all of the circuit elements must be
robust or there is some inherent circuit impedance at 60 Hz
to limit current flow (the latter is unlikely for high speed
digital circuits).  In this case, §NAC.2.3 doesn't require
use of a wiring simulator, but if the circuit doesn't
contain overcurrent protection, the product may not comply.

> Have I overlooked some requirement or does the standard
> avoid addressing this problem? Is there a suggested
> solution: The only one I can think of is adding a ground
> at the service entrance and fusing the shield, but this
> is not a current practice.
>
> Bob Johnson
> ITE Safety

Fusing the shield doesn't make sense.  Fusing the center
conductor does.



Regards,

Peter L. Tarver, PE
[email protected]



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ieee-pses.org/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]