From: [email protected] [mailto:[email protected]]
Sent: Thursday, November 27, 2003 6:55 PM
To: [email protected]
Subject: 400 Hz filter


Hi All,
 
looking for a filter for a shield room. Needs to be 400 Hz capable, and good
for 230 Vac if possible. Anything above 30 Amps would be good.
 
Anyone have one lying about on the shelf?
 
Thanks,
 
Derek N. Walton
Owner, L F Research EMI Design and Test Facility
Poplar Grove,
IL 61065 
 

 
Derek:
 
When you say "400 Hz capable", it sounds like you intend to use it with other
power frequencies (DC, 50 Hz, 60 Hz) as well as 400 Hz. Remember that at 400
Hz, the capacitive line current may be very significant (>10 amps), and the
usual remedy for this is a "power factor correction coil" for each filter
line. (The inductive reactance is adjusted to match the capacitive reactance,
creating a parallel resonant "tank" circuit. Line current will drop
significantly.)
 
If you use the filter just for 400 Hz, you can leave the PF coils permanently
connected. OTOH, if you use it for 60 Hz (or lower), then you might want to
make the coil "switchable", so you can disconnect it.
 
Regards,
 
Ed
 

Ed Price 
[email protected]         WB6WSN 
NARTE Certified EMC Engineer & Technician 
Electromagnetic Compatibility Lab 
Cubic Defense Applications 
San Diego, CA  USA 
858-505-2780  (Voice) 
858-505-1583  (Fax) 
Military & Avionics EMC Is Our Specialty 

 