20kA at 10kV probably cannot be done effectively -- this implies a source
impedance of the generator of only 0.5 ohms. So far no problem, but what
happens when you add any kind of load ? The available current into a 0.5 ohm
load is only 10kA; into a 0.1 ohm load it's only 16.7kA....
 
But that's not the only problem: with the 8/20us waveform, the di/dt at 20kA
says that the inductance of wire will have an effect: V drop (across a piece
of wire)  = Ldi/dt: the available current is then 10kV/(0.5 ohms + the
effective impedance of the inductor with the 8us rise time) --- if you assume
0.1uH/10cm of #20 wire (use your own numbers if you think I'm wrong) the
current is then 19kA if the resistance is 0 ohms for 10cm of wire........
smaller wire is worse, bigger wire helps, but someone told me once that
building steel is considered to be about 0.1uH/foot, so maybe that's worst
case....
 
All of that only says that to get 20kA into a cable of any length at all will
require a generator with a much higher compliance voltage --- at least 40kV
and a 2 ohm source......  Certainly out of our ballpark at Thermo...
 

Best Regards, 

Michael Hopkins 
Manager, EMC Technologies 
Control Technology Division 
Compliance Test Solutions 
Thermo Electron Corporation 
One Lowell Research Center 
Lowell, MA 01852 
Tel: +1 978 275 0800 ext. 334 
Mobile: +1 603 765 3736 
[email protected] 


One Thermo, committed to integrity, intensity, innovation & involvement 


From: Roger Hsu [mailto:[email protected]]
Sent: Tuesday, March 23, 2004 11:02 PM
To: [email protected]; [email protected]
Subject: 10kV/20kA 8/20us surge



All, 

Does any one know a test lab that can perform the 10kV/20kA 8/20us-current
surge for the DC power supply.  Is this requirement same as GR-1089:2002 R4-45
requirement? (GR-1089:2002 R4-45 did not mention the test voltage) 

I also need to look for the manufacturer for the above surge generator. 

Thanks and regards, 

Roger