This is a multi-part message in MIME format.
John, are you sure? I'm looking at 7.0 of EN 61000-3-2:2000 and it states:

"For the following categories of equipment limits are not specified in this
edition of the standard. 
NOTE 1: Limits may be defined in a future amendment or revision of the
standard:
- Equipment with a rated power of 75W or less, other than lighting equipment, 
NOTE 2: This value may be reduced from 75W to 50W in the future, subject to
approval by National Committees at that time.
- Professional equipment with a total rated power greater than 1kW;
- Symmetrically controlled heating elements with a rated power less than or
equal to 200W;
- Independent dimmers for incandescent lamps with a rated power less than or
equal to 1kW."

I read this to say that any classification of equipment, other than lighting
equipment, with a rated power less than 75W has no specified limits.

Jim Hulbert
Pitney Bowes

 John Woodgate <[email protected]>






        John Woodgate <[email protected]> 
Sent by: [email protected] 

        05/01/2004 07:42 AM 

        

        Please respond to
John Woodgate <[email protected]>

 


To

[email protected]     



cc

        



Subject

Re: EN 61000-3-2        
                


I read in !emc-pstc that [email protected] wrote (in
<[email protected]>)
about 'EN 61000-3-2' on Thu, 29 Apr 2004:
>    For class A equipment, harmonic limits are not specified for 
>    equipment with a rated power of 75W or less. 

No, that's Class D. For Class A, the limits are expressed as currents,
and apply at any 'rated power'. 


<<graycol.gif>>

<<ecblank.gif>>

Reply via email to