Richard,

By ratio, I mean how many CO in % contains the DC mains supply within a
single building and connect the supply to building's earth. My thought was
that 99% of the CO were doing it.

Regards,

Alexandre Deneault
Spécialiste de certification/Certification specialist

Kontron Canada Inc.
616 Cure-Boivin
Boisbriand, Qc Canada
J7G 2A7
Tél: (450) 437-4661, Ext:2449
Fax: (450) 437-8053

E-mail : <mailto:[email protected]>
Web:   http://www.kontron.com



> -----Original Message-----
> From: [email protected] [SMTP:[email protected]]
> Sent: Monday, August 16, 2004 1:35 PM
> To:   [email protected]; [email protected]
> Subject:      Re: DC mains supply vs transients in centralized office
>
> Alexandre,
>
> I am unclear what you are asking when you speak about the 'ratio'.
>
> Creepage distances are determined by the long-term voltage across the
> insulation, so consideration of transient voltages are irrelevant.
>
> For determination of clearances, knowledge of the transient voltages is
> important.   As you said, IEC 60950-1 tells you what value to assume (zero
> volts) and so in terms of compliance with this safety standard you can
> determine what clearance is required - providing the conditions specified
> in the standard are met [i.e. a) the DC mains supply is contained within a
> single building and b) 0V of the supply is connected to the building's
> earth): if these conditions are not met then the voltage could be very
> high and could potentially vary from installation to installation].
>
> Of course, many customers will have their own requirements for expected
> transient voltages and your design will need to accommodate these from a
> functionality perspective.  There are also what I consider to be
> generalised customer requirements published by Telcordia in the USA and
> ETSI in Europe.   The point here is that these values are probably most
> important in determining the type and rating of transient suppression
> component rather than determining the value of transient voltage to be met
> for those standards required for certification purposes.  After all, if
> your transient suppression components are doing their job correctly then
> the voltage measured in your equipment will be substantially lower than
> the open circuit voltage applied by the surge generator.
>
>
> Regards,
>
> Richard Hughes
>
> In a message dated 08/16/2004 16:33:39 GMT Standard Time,
> [email protected] writes:
>
>       Hi,
>
>       IEC60950-1 says "for equipment to be supplied from a DC mains supply
> that is
>       connected to protective earth and is entirely within a single
> building, the
>       mains transient voltage is considered to be zero."
>
>       In order to avoid over-designing in regards with, clearances,
> creepage
>       distances, electric strength test, etc... could someone provide a
> ratio for
>       centralized office (using centralized DC mains) respecting both
> conditions
>       mentioned above.
>
>       Thanks!
>
>       Alexandre Deneault
>
>



This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.

IEEE PSES Main Website:  http://www.ieee-pses.org/

To post a message send your e-mail to [email protected]

Instructions for use of the list server:

    http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to