John,

It occurred to me I did not mention that you cannot connect Y loads to a
system of this sort since the neutral is not balanced.
In theory you could run a Y connected motor with the center connection
floating. I have never tried it but it sound reasonable. Y connected motors
are pretty unusual anyway.

Bob


From: [email protected]
[mailto:[email protected]] On Behalf Of John McAuley
Sent: Monday, July 26, 2004 11:44 AM
To: Robert Johnson; 'EMC-PSTC (E-mail)'
Subject: RE: Three Phase Power in Belize

http://www.ieee-pses.org/symposium
          http://www.emc2004.org/


Robert

This is exactly what I was looking for. It fits the results of the
measurements that were made.

Thank you very much.

John




From: Robert Johnson [mailto:[email protected]]
Sent: 26 July 2004 14:44
To: [email protected]; 'EMC-PSTC (E-mail)'
Subject: RE: Three Phase Power in Belize


The world power description tables (see http://www.safetylink.com/)are not
much help on three phase.

What you describe sounds like a three phase center grounded delta supply.
Belize standard voltages are 100/220V 60 Hz. I'll assume 120/240V for your
case.
That means a center tap on one leg of the delta is grounded. This provides
120v from neutral to phase A and 120 volt neutral to phase B, with 240V
phase A to B (conventional household supplies)
The third phase, C, is 240 volts from A or B and 208 volts from neutral
(thus the term high line). Often the supply is done with only two
transformers, omitting a supply transformer for phase A-C to save costs but
with reduced power and slightly less balanced phase voltages (you can ignore
that fact).
This means you actually have a 240 volt three phase supply, not a 208 volt
one.
Let's see if I can draw a crude text vector diagram.

              C
             /|\
            / | \
           /  |  \
          /   |   \
         /    |    \
        /     |     \
      240    208    240
      /       |       \
     /        |        \
    A---120---N---120---B
      -------240-------
Keep in mind, the info you provided is not near enough to assure a match
with what I described above.

In any case, if you have three phases 240 volts apart, you can simply
connect delta loads wired for 240 without much worry. Likewise for 208
volts.

Bob Johnson
ITE Safety


From: [email protected]
[mailto:[email protected]] On Behalf Of John McAuley
Sent: Monday, July 26, 2004 6:45 AM
To: EMC-PSTC (E-mail)
Subject: Three Phase Power in Belize

http://www.ieee-pses.org/symposium
          http://www.emc2004.org/


Dear Group

A friend of mine is doing development/charity work in Belize and is trying
to hook up some old lathes, milling machines etc of European origin to their
supply. He has limited electrical knowledge being from a mechanical
background.  He tells me that the supply is "high line".  Apparently this
means that they have two phases at 120 V and a third line at 208 V!!
Apparently there are 3 phase machines already running on this supply. He has
measured the phase voltages and  has confirmed the levels. The machines were
rewired for a 120V/208V system.

Is anyone familiar with this connection system? Is there a voltage offset on
the neutral? I can't find reference to it on the internet. I would like to
be in a position to teach him how the identify the phase voltages so that he
can connect up the machines without generating any more smoke.

Many Thanks

John McAuley



This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.

IEEE PSES Main Website:  http://www.ieee-pses.org/

To post a message send your e-mail to [email protected]

Instructions for use of the list server:

    http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc



This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.

IEEE PSES Main Website:  http://www.ieee-pses.org/

To post a message send your e-mail to [email protected]

Instructions for use of the list server:

    http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc



This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.

IEEE PSES Main Website:  http://www.ieee-pses.org/

To post a message send your e-mail to [email protected]

Instructions for use of the list server:

    http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to