http://www.ieee-pses.org/symposium http://www.emc2004.org/
-------------------------------------------------- 

All,

 

The horse is dead, beaten, turned into glue (probably a few McDonald’s
hamburgers) and buried :-)

 

David Sterner and I have bounced a few emails back and forth (offline) on the
subject.  We discussed OHSA, EN 61000-4-2 and some individual test setups. 
Just to clarify for the benefit of the group.

 

Most ESD setups require the 940Kohm resistance from the coupling planes (HCP
or VCP)  to ground.

 

-The resistors complete the circuit from ESD gun to GRP through the coupling
plane, allowing for potential equalization (charge bleeding) between
discharges.  This makes repeatable test results.

 

-The high value of the resistors protects the test personnel in the following
instance:  if the test tech touches a hazardous voltage in the EUT with one
hand and touch the coupling plane with the other hand; then the high
resistance to ground will limit the current through the tech’s chest cavity
(the worst possible area for hazardous current to flow).     On the other
hand, if the coupling plane was grounded, or bonded to ground with a low
resistance, there would be a dangerous current through the tech’s chest
cavity.    This is OSHA’s peeve with grounded conductive tabletops.  David
was more enlightened regarding the OSHA requirements, so this is a tidbit that
I didn’t have.

 

-Having said all of that, if the tech touches a hazardous voltage or if the
coupling plane becomes charged, the resistors will not protect the tech from
the hazardous voltage going to ground through his feet or through his bottom
to a metal chair…  This is why you still have to use caution, even with the
resistors installed.

 

 

Although the initial email just asked about the power rating (which we mostly
agree to be ¼ Watt, up to 15KV).

 

 

Another point that I haven’t seen is with regard to the length of the
resistors.  A good rule of thumb is to require 1mm of air space to insulate
1KV of ESD.  So, just make sure that your resistors are long enough from
terminal to terminal to insulate the expected ESD voltage of your test setup.

 

For example, if you plan on going up to 15KV, and you use two 470Kohm
resistors; then each resistor is subjected to 7.5KV….which would imply that
the resistor body should be 7.5mm (about ¼ inch) long in order to prevent the
ESD from jumping over.  Shorter resistors could be potted (RTV,
varnish…whatever you have handy) to help out.  This may also be part of the
reason that Dave C. from Micron mentioned the 2W resistors.  They would be
plenty long enough to handle higher ESD voltages without flashover.

 

 

Chris Maxwell

Design Engineer

Nettest

------------------------------------------- 

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. 


IEEE PSES Main Website: http://www.ieee-pses.org/ 


To post a message send your e-mail to [email protected] 


Instructions for use of the list server: 


http://listserv.ieee.org/listserv/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Ron Pickard: [email protected] Dave Heald: [email protected] 


For policy questions, send mail to: 


Richard Nute: [email protected] Jim Bacher: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


Reply via email to