I took some test data.  That may be a bit of an exaggeration, but I made a
few measurements.

This was at one of the electrical outlets where I got a one-handed shock.
It is also where the electrolyte content of the rug is unknown but possibly
not zero, on account of the four-legged members of this family are not as
well-trained as I might hope.

I measured the line potential phase-to-neutral and phase-to-ground and it
was 118-120 Vac.

I then configured the Triplett 9005 DMM as an ammeter, and connected from
phase to floor.  I measured to rug, then poked hard and ran the probe point
into the sub-floor.  I measured zero on scales 2 ma and 200 uA full-scale.

I then went back to voltmeter mode and measured phase-to-floor potential.
About 20 Volts.  I removed the ground lead, so that the voltmeter had a
single connection to phase, and just capacitance to ground.  Reading dropped
to around 6 Vac.  I grabbed the voltmeter and the reading rose to about 10
Vac.  I squeezed hard and the reading went to 18 Volts.  I placed a fat
pillow on the floor and stood on it and the reading went down a little.  I
am wearing socks but no shoes at this point.

Then I decided to quit messing around.  I connected the ground lead back to
the voltmeter and grabbed the probe end while standing on the floor.  The
reading rose to 60 Vac.  I got back on the pillow and the reading dropped a
little.

This is looking an awful lot like capacitance, folks.

I think I can quantify the amount of capacitance.  Standing on the floor in
socks, the meter reads 60 Volts, or half the line potential when I grab the
negative lead.  That means that roughly half the line potential drops across
the meter, and half drops across me and my path to ground.  I don't have a
manual for this meter, and specs on the internet don't show input impedance,
but I think most DMMs are in the neighborhood of 10 MOhms.  If that is a
good number, then I and my path to ground were also 10 MOhms.  At 60 Hz,
that means a capacitance of 265 pF, which seems reasonable.  In my shoes,
the measured potential was 50 Volts, which means that the capacitance
dropped to 220 pF.

The implication is that about 6 uA of current was passing through me, and of
course I couldn't feel it.  But there is still a problem.  If I left the
voltmeter out of the circuit and grabbed the phase potential directly I
would get the one-handed shock.  But according to these numbers, the voltage
would of course double to 120 Volts, and the current would double to 12 uA.
I don't think that would be enough to tickle me, let alone be sensed as
shock.  I have a feeling it has something to do with the difference in
source impedance, but I can't put my finger on it.  I think the line
potential could cause electrical ionization in my body that was not
occurring with 60 Volts across me from a 10 MOhm source impedance.  But if
my body has a capacitance of 200 pF to ground, then it shouldn't really
matter if my body looks like a few kOhms at low potential, or a dead short
at high potential - the 200 pF is the limiting factor, not the body
resistance.

Comments?


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Ron Pickard:              [email protected]
     Scott Douglas             [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to