Last version of EN 301 489-1 version 5 is know in line with CISPR/EN500024.

The test level for telecommunications ports, intended to be directly connected
to the telecommunications network via
outdoor cables, shall be 1 kV line to ground as given in EN 61000-4-5 [11],
however, in telecommunications centres
0,5 kV line to ground shall be used. In this case the total output impedance
of the surge generator shall be in accordance
with the basic standard EN 61000-4-5 [11].
The test generator shall provide the 1,2/50 µs pulse as defined in EN
61000-4-5 [11].


This version was just published by ETSI the 16 of November 2004.

Paolo

_________________________________________________

Paolo Gemma

Siemens Mobile Communications  S.p.A.

SMC PG MW ST EMC & Safety

SS Padana sup. KM 158 20060 Cassina de' Pecchi (MI) Italy

phone +39 02 9526 6587    fax +39 02 9526 6375

mobile +39 348 3690185

e-mail [email protected]

_________________________________________________



> -----Messaggio originale-----
> Da: Carpentier Kristiaan [mailto:[email protected]]
> Inviato: mercoledì 24 novembre 2004 15.27
> A: Gemma Paolo; [email protected]; [email protected]
> Oggetto: RE: Definition of Telecommunication port
>
>
> Paolo,
>
> I agree with you that ethernet port shall be tested for Cond.
> emission but it is strange to see that the immunity standard
> CISPR24/EN55024 only requires SURGE testing on telecom ports
> connected to outdoor cabling while EN301489-1 makes no
> differences between telecom ports connected to indoor or
> outdoor cables for SURGE testing. Do you know if Ethernet
> ports are also excluded from Surge testing if EN301489-1 is
> applied ? Regards, Kris
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]On Behalf Of Gemma Paolo
> Sent: woensdag 24 november 2004 14:55
> To: [email protected]; [email protected]
> Subject: R: Definition of Telecommunication port
>
>
> The last definition in CISPR 22 is:
> 3.6
> telecommunications/network port
> point of connection for voice, data and signalling transfers
> intended to interconnect widelydispersed systems via such
> means as direct connection to multi-user telecommunications
> networks (e.g. public switched telecommunications networks
> (PSTN) integrated services digital networks (ISDN), x-type
> digital subscriber lines (xDSL), etc.), local area networks
> (e.g. Ethernet, Token Ring, etc.) and similar networks NOTE A
> port generally intended for interconnection of components of
> an ITE system under test (e.g. RS-232, IEEE Standard 1284
> (parallel printer), Universal Serial Bus (USB), IEEE Standard
> 1394 ("Fire Wire"), etc.) and used in accordance with its
> functional specifications (e.g. for the maximum length of
> cable connected to it), is not considered to be a
> telecommunications/network port under this definition.
>
>
> A ethernet interface is a telecommunication port if the
> interface is a real ethernet interface in line with IEEE
> standards, there is no limitation on the lenght of cable. The
> questions is not on the number of Equipment attacched to the
> network but on the lenght of the wire/network. Ciao paolo
>
> _________________________________________________
>
> Paolo Gemma
>
> Siemens Mobile Communications  S.p.A.
>
> SMC PG MW ST EMC & Safety
>
> SS Padana sup. KM 158 20060 Cassina de' Pecchi (MI) Italy
>
> phone +39 02 9526 6587    fax +39 02 9526 6375
>
> mobile +39 348 3690185
>
> e-mail [email protected]
>
> _________________________________________________
>
>
>
> > -----Messaggio originale-----
> > Da: [email protected]
> > [mailto:[email protected]] Per conto di
> > [email protected]
> > Inviato: martedì 23 novembre 2004 23.40
> > A: [email protected]
> > Oggetto: Definition of Telecommunication port
> >
> >
> > In EN55022 / CISPR 22 the definition of a telecommunication port is:
> >
> > "Ports which are intended to be connected to telecommunication
> > networks (e.g. public switched telecommunication networks,
> integrated
> > digital networks), local area networks (e.g. Ethernet,
> Token Ring) and
> > similar networks".
> >
> > We have an ITE with an Ethernet port to communicate with a
> PC or many
> > PCs. Do we here talk about an Ethernet LAN and therefore is our
> > Ethernet port classified as a telecommunication port?
> Intended use for
> > our equipment is for consumer and Small Office, Home Office (SOHO).
> >
> > The reason for asking is that conducted emission and surge
> apply for
> > telecommunication port under the standard EN 301 489-1.
> >
> > Thanks.
> >
> > Regards
> > Amund Westin,
> > Oslo / Norway
> >
> > ----------------------------------------------------------------
> > This message is from the IEEE Product Safety Engineering Society
> > emc-pstc discussion list.    Website:  http://www.ieee-pses.org/
> >
> > To post a message to the list, send your e-mail to [email protected]
> >
> > Instructions:
> > http://listserv.ieee.org/listserv/request/user> -guide.html
> >
> >
> > List rules:
> > http://www.ieee-pses.org/listrules.html
> >
> > For help, send mail to the list administrators:
> >
> >      Ron Pickard:              [email protected]
> >      Scott Douglas             [email protected]
> >
> > For policy questions, send mail to:
> >
> >      Richard Nute:           [email protected]
> >      Jim Bacher:             [email protected]
> >
> > All emc-pstc postings are archived and searchable on the web at:
> >
>     http://www.ieeecommunities.org/emc-pstc
>
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society
> emc-pstc discussion list.    Website:  http://www.ieee-pses.org/
>
> To post a message to the list, send your e-mail to [email protected]
>
> Instructions:
> http://listserv.ieee.org/listserv/request/user> -guide.html
>
>
> List rules:
> http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
>
>      Ron Pickard:              [email protected]
>      Scott Douglas             [email protected]
>
> For policy questions, send mail to:
>
>      Richard Nute:           [email protected]
>      Jim Bacher:             [email protected]
>
> All emc-pstc postings are archived and searchable on the web at:
>
    http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Ron Pickard:              [email protected]
     Scott Douglas             [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to