Good points - I would only say that I was mainly addressing Jim's original
question about the rating of the double-socket itself in respect of BS1363,
and not really the wider issue of Socket/cable/MCB coordination.

Regards

John

From: "Nick Williams" <[email protected]>
To: "John Allen" <[email protected]>
Cc: "Colgan, Christopher [Harman Pro Group UK]"
<[email protected]>; <[email protected]>
Sent: Tuesday, April 05, 2005 10:54 AM
Subject: Re: UK Domestic Electrical Socket Outputs


> With all due respect to everyone who has commented so far, I think
> you have all missed a fundamental point (although John got quite
> close to it).
>
> So long as the MCB (or fuse) in the fuseboard is correctly specified
> for the cable(s) which connects it to the socket, then the rating of
> the socket itself is largely irrelevant. After all, you can have more
> than one double gang socket on a ring main, and the total load can be
> anything up to the 30A rating of the MCB.
>
> A ring main is rated at 30A despite the fact that it only used 2.5mm
> sq cable because two cables (=5mm sq) are used.
>
> So, in practice, the total load on a double gang socket can be 2 x
> 13A = 26A on a ring main, but only 15A on a spur. The limiting factor
> in the first case is the fusing of the plugs, in the second case it's
> the fusing of the fixed wiring.
>
> It's a question of what is the weakest link in the chain.
>
> Nick.
>
>
>
> At 6:02 pm +0100 4/4/05, John Allen wrote:
> >Chris, Jim
> >
> >Just taken a look at BS 1363-2: 1995, which is the part dealing with
> >sockets - the results are interesting!
> >
> >Here are the most relevant bits (with an awful lot left out!)
> >
> <snip>
>
>


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to