Interesting thread; educational.  There's the pure science of the issue and
there's the regulatory expedient solution.  Interestingly, the FCC mandates
using a loop for frequency measurements below 30 MHz, but gives the limit in
dBuV/m.  The antenna factors of the loop antennas are typically given for
both E and H field related by far field factor of 51 dB.  As indicated
before, 50 kHz is anything but far field, and one will not be able to
measure the H field of a loop source of 50 kHz in the far field.  

So as Cortland pointed out, precise and inaccurate it is...

Don Umbdenstock
Manager Compliance Engineering
 
Tyco Safety Products / Sensormatic
6600 Congress Avenue
Boca Raton, FL  33487 USA
561.912.6440
[email protected]
 


From: Bob Richards [mailto:[email protected]] 
Sent: Friday, June 24, 2005 8:05 AM
To: [email protected]
Subject: Re: ??? RE: ??? RE: Near field H-field measurement.

Ken,

I'm no expert, but as I understand it, making
measurements at low frequencies, measured in the near
field, it is possible to have a very high E-field and
very low H-field if the radiating source is high
impedance. The opposite is true if the radiating
source is low impedance, ie: high H-field, low
E-field.

Also, if the coupling mechanism of the susceptible EUT
is primarily inductive, (low impedance) then a
high-impedance radiator will be less likely to cause
interference than a low-impedance radiator.

If my understanding is correct (tell me if I am wrong)
then I can see the case for making low-frequency
radiated emissions measurements with both E-field
whips and H-field loops, with a limit specified for
each, such as is done for GR1089 testing.

There also needs to be some insurance that the
immunity tests cover these two scenarios as well. I
wonder just how well the conducted immunity tests
relate. The 61000-4-3 test (with CDNs) is with a fixed
source impedance of 150 ohms. Theoretically there can
only be a 6dB increase in either current or voltage if
the EUT port has a very low or very high impedance.

Bob Richards, NCT.



--- Ken Javor <[email protected]> wrote:

> In my opinion...
> 
> The right limit is the limit which protects
> reception of broadcast signals
> in licensed bands.  At low frequencies where the
> "antenna" is either a loop
> or whip, the limit would be ascertained using a
> typical loop/whip connected
> to a typical receiver.  The most accurate limit
> would be the rfi level at
> the receiver antenna port that allows a specified
> quality of reception in
> the presence of the rfi.  The measurement would be
> made at a specified
> distance from the rfi source.   The limit would then
> be so many dBuV or dBm
> in a certain bandwidth, using a particular
> loop/whip.  The loop/whip
> construction and transducer factor would have to be
> specified.
> 
> This is the only technically proper way of doing
> things until you are at a
> frequency/distance from rfi source such that a far
> field measurement is
> possible.  A field intensity limit allowing the use
> of any suitable antenna
> is only appropriate if a far field measurement is
> possible.
> 


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas             [email protected]
     Mike Cantwell            [email protected]

For policy questions, send mail to:

     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to