Nick,

For what it's worth, I took the IEE BS7671 Design course a few years ago.
In one exercise, you were quoted by the electrical supplier a prospective
short circuit current Ip  of 25kA (3 phase) "in the road", and you have to
calculate a more realistic value of Ip at the origin of the installation.
You calculate Zphase ... divide 400 V by sqrt 3 and Zphase... and the answer
was 12.83 kA.

I would guess that you get quoted values of interrupt current from the power
utilities, just as you do in North America, and you would expect them to be
on the order of tens of kAs.

Regards,


Don Gies, N.C.E
Senior Product Compliance Engineer
Lucent Technologies
Holmdel, NJ 07733 USA


From: Nick Williams [mailto:[email protected]]
Sent: Tuesday, October 18, 2005 4:49 AM
To: [email protected]
Subject: Domestic electrical supply fault currents


Can someone point me to a resource which gives typical maximum fault
currents available from a domestic electrical supply in the UK?

BS 7671 discusses the issue and gives methods for calculation of
temperature rise under fault conditions, as well as maximum fault
clearing times, but it doesn't appear to give any numbers for the
fault currents. I have no feel for what sort of numbers  are actually
involved although I suspect that it will be in the kA range.

Rgds

Nick.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to