Dear Group Members,
 
Can someone explain what the meaning of "A maintained-break type switch shall
open all ungrounded conductors" is?  This is from the following paragraph:
 
===============================================================================

29 Test Switch

 

29.1 Emergency lighting and power equipment provided with an automatic load
control switching device

shall be provided with a manually operable test switch, or provisions for the
connection of an external test 

switch, to simulate the conditions under which the load control switching
device is intended to operate

(such as loss of the normal supply).

29.2 The test switch may be the maintained-break type, in which case it shall
be accessible only to

authorized persons. A maintained-break type switch shall open all ungrounded
conductors .

29.3 For the purpose of meeting the requirement in 29.2, a test switch is
considered accessible only to

authorized persons if it is mounted within an enclosure, or if it is of the
key-operated type. If the test switch 

is mounted within an enclosure, the cover of the enclosure shall be hinged in
accordance with 8.7.1 –

8.7.4

===============================================================================
 
Thank you for your time and look for your help.
 
Best regards,
Grace Lin
Crestron Electronics, Inc.
New Jersey, USA
www.crestron.com
- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________



Reply via email to