The IEC 61000-4-6 standard allows for calibrations to be done into 300 ohm or
100 ohm loops (or 150 ohm & 50 ohm terminations).  Using the 150 ohm
termination, the calibration is done by leveling from the formula Um=U0/6. 
This is done with the 6 dB attenuator in place.  Performing this calibration,
determines the power levels necessary of the amplifier to achieve the voltage
Umr.   But in the test mode, using the BCI clamp as well as the 6 dB
attenuator, the test is performed while monitoring with a current measuring
probe to avoid over-injection.  As you mentioned, the formula U0/150 ohms will
limit the current.  

 

So during calibration using the 150 ohm termination setup, the voltage
measured Umr= U0/6,   so for level 3,  Umr =1.66 V.  This would yield 33 mA of
current across the 50 ohm resistor.  But during test, Imax= U0/150 yields 66
mA of current.  

 

Regards,

Rodger Gensel

AR RF/Microwave Instrumentation

 

  _____  

From: [email protected] [mailto:[email protected]] On Behalf Of Bob Richards
Sent: Thursday, April 12, 2007 8:59 AM
To: ieee
Subject: Questions on 61000-4-6 conducted immunity

 

I've been doing some research on the IEC 61000-4-6 standard, and have a couple
of questions that hopefully someone here can answer.

 

What is the rationale behind specifying the test level as Vemf (open circuit
voltage)? The calibration is actually done to 1/2 the test level since the
calibration fixture is terminated.

 

When performing clamp injection according to section 7.4, the injected current
is monitored and limited by the formula Imax = Uo/150.  Since the test level
Uo is specified as an open circuit voltage, and the terminated calibration
level is 1/2 Uo, would this not allow the EUT to be overtested by 6dB?

 

Bob Richards, NCT.

 

- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators: 

Scott Douglas [email protected] Mike Cantwell [email protected] 

For policy questions, send mail to: 

Jim Bacher: [email protected] David Heald: [email protected] 

All emc-pstc postings are archived and searchable on the web at: 

http://www.ieeecommunities.org/emc-pstc


______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________

- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to [email protected] 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas [email protected] Mike Cantwell [email protected] 


For policy questions, send mail to: 


Jim Bacher: [email protected] David Heald: [email protected] 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


Reply via email to