Hi Brian:

If the neutral is grounded at two points or more, then the 
earth is in parallel with the neutral and will carry some portion
of the neutral current that flows between those two points.

This current will cause a potential difference (voltage)
between two points of the earth near or on the current 
pathway.

The NEC requires the neutral to be grounded at the service
entrance to a building.  If the supply to two buildings is from
the same source, then some portion of the neutral current 
will flow through the earth between the two buildings.

Of course, a copper neutral wire likely has much lower 
resistance than the earth.  Nevertheless, current will 
flow through the earth, especially if the earth is highly 
conductive between the two ground points.


Best regards,
Rich

-