Hello Aboo,

The overvoltage category is based on the transients that you are likely to
see on the line voltage.  Overvoltage Category II assumes that lightning
transients will be attenuated by step-down transformers and the impedance
within the building's power wiring.  However, if you are making a new
connection outside the building, that wiring may be exposed again to higher
transients.  You need to look at the installation of the camera to see how
the power wiring is protected.  If it has little protection, it probably
should be considered Overvoltage Category III.  If this is the case, it may
also allow transients to come directly into the building wiring through the
camera's power.

I have seen problems with this type of installation in lightning prone
areas.  For example, I don't recommend installing items on the top of a
pole in central Florida unless you are ready for direct lightning strikes.

Ted Eckert
APC-MGE
http://www.apc.com/

The items contained in this e-mail reflect the personal opinions of the
writer and are only provided for the assistance of the reader. The writer
is not speaking in an official capacity for APC-MGE or Schneider Electric.
The speaker does not represent APC-MGE's or Schneider Electric's official
position on any matter.


                                                                           
             "aboo, chang"                                                 
             <[email protected]                                             
             >                                                          To 
             Sent by:                  [email protected]                   
             [email protected]                                          cc 
                                                                           
                                                                   Subject 
             04/14/2008 08:30          About overvoltage category          
             AM                                                            
                                                                           
                                                                           
                                                                           
                                                                           
                                                                           







Hi experts..

I have some questions about overvoltage category..

According to IEC 60664 and 60364 definition, overvoltage III
means:Equipment that will be an integral part of the building wiring,
overvoltage II means:PLUGGABLE or PERMANENTLY CONNECTED EQUIPMENT that will
be supplied from the building wiring.

My question is, if a equipment is installed in outdoor location, for
instance, a camara installed upon telephone pole, its power is from
building soket(plug A type, overvoltage category II), can we also consider
this outdoor equpment as overvoltage II? Or we must define it as
overvoltage category III because it is outside building and maybe infected
by lightning?

Thanks
Aboo...


- ---------------------------------------------------------------- This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/


To post a message to the list, send your e-mail to [email protected]


Instructions: http://listserv.ieee.org/request/user-guide.html


List rules: http://www.ieee-pses.org/listrules.html


For help, send mail to the list administrators:


Scott Douglas [email protected] Mike Cantwell [email protected]


For policy questions, send mail to:


Jim Bacher: [email protected] David Heald: [email protected]


All emc-pstc postings are archived and searchable on the web at:


http://www.ieeecommunities.org/emc-pstc

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to