I'm looking for some help in identifying some specific requirements  
for the earthing of small generators (engine driven, say 5 - 10 kVA).

For reasons which I'm not entirely clear about, the client wishes to  
sell a 230V generator with the earth connection made to a mid point on  
the generator windings instead of one end, i.e. with respect to ground  
the output will be 115V - 0V - 115V instead of being 0V - 230 which  
would be normal.

I'm trying to find good reasons to say why this is not permitted.  
Clearly the UK supply Regulations do not permit such an arrangement,  
but I don't think these would apply to a small generator. I have also  
identified that BS 7375 (Distribution of electricity on building  and  
construction sites) says that a generated supply should be treated in  
the same way as a utility supply, and BS 7430 (Code of practice for  
earthing) recommends the use of an earthed neutral for 230V or three  
phase 400V generators. However, neither of these constitute what I  
would consider to be an unequivocal 'thou shalt not do it'.

HSE publish a guide on electrical safety on construction sites but  
this essentially refers back to BS BS 7375 and BS 7430 for detailed  
guidance.

 From a safety point of view, the generator will be fitted with a  
residual current breaker and since in practice few small portable  
generators are ever actually properly grounded, it seems to me that  
the main safety concern is that it's not normal practice to do it this  
way and it only becomes dangerous when the generator is connected to a  
network designed with neutral point earthing. This may be sufficient  
reason to say it's not a sensible proposal, but if it is then I need  
to be clear on the point, not simply say it can't be done for un- 
specified 'safety' reasons.

Can anyone else offer any insight into (a) any specific requirements  
which may govern this practice and (b) and reasons why it's actually  
unsafe?

Thanks

Nick.

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.    Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to [email protected]

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

     Scott Douglas           [email protected]
     Mike Cantwell           [email protected]

For policy questions, send mail to:

     Jim Bacher:             [email protected]
     David Heald:            [email protected]

All emc-pstc postings are archived and searchable on the web at:

    http://www.ieeecommunities.org/emc-pstc

Reply via email to