Context is a simple, two winding transformer evaluated against the
requirements in the 60950-1 standards. (The following reflects descriptions
of transformers in some test reports I have reviewed.)
Consider:
1) Double Insulation or Reinforced Insulation is required between
windings .
2) A three flanged bobbin that meets the through insulation
requirements for
Reinforced Insulation.
3) Double Insulation consists of Basic Insulation plus Supplementary
Insulation.
4) AWM is used for one of the two windings.
5) A Creepage Distance is provided between primary and secondary
windings
over the center flange that is at least half that otherwise required to meet
Reinforced Insulation.
6) The AWM in 4 is declared to provide Basic Insulation, while the
Creepage
Distance in 5 is declared to provide Supplementary Insulation.
7) 6 is rejected by a safety certifier and the AWM insulation is
forced to
meet Supplementary Insulation. However, because the AWM insulation thickness
is less than 0.4 mm thick, the construction is considered noncompliant.
Similar arbitrary declarations of compliance or noncompliance, are, I'm
certain, a common experience among readers of this list. Other than an
approach that infers that the whim of the safety certifier wins the day, if
their certification is to be applied to a product, what rationale have others
experienced under similar scenarios?
Regards,
Peter L. Tarver, PE
[email protected]
CONFIDENTIALITY
This e-mail message and any attachments thereto, is intended only for use by
the addressee(s) named herein and may contain legally privileged and/or
confidential information. If you are not the intended recipient of this e-mail
message, you are hereby notified that any dissemination, distribution or
copying of this e-mail message, and any attachments thereto, is strictly
prohibited. If you have received this e-mail message in error, please
immediately notify the sender and permanently delete the original and any
copies of this email and any prints thereof.
ABSENT AN EXPRESS STATEMENT TO THE CONTRARY HEREINABOVE, THIS E-MAIL IS NOT
INTENDED AS A SUBSTITUTE FOR A WRITING. Notwithstanding the Uniform
Electronic Transactions Act or the applicability of any other law of similar
substance and effect, absent an express statement to the contrary hereinabove,
this e-mail message its contents, and any attachments hereto are not intended
to represent an offer or acceptance to enter into a contract and are not
otherwise intended to bind the sender, Sanmina-SCI Corporation (or any of its
subsidiaries), or any other person or entity.
-
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. Website: http://www.ieee-pses.org/
To post a message to the list, send your e-mail to [email protected]
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas [email protected]
Mike Cantwell [email protected]
For policy questions, send mail to:
Jim Bacher: [email protected]
David Heald: [email protected]
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc