Hi Donald:

A VDR is taken as a device that is likely to
fail.

If the VDR is connected between mains and the
protective earthing system, then the PE system
must be considered reliable, that is, equivalent
to a reinforced safeguard.

Ever since the days of 2-wire plugs and sockets,
grounding by means of a domestic plug and socket
has not been considered reliable (because you
could not predict whether the installation was
2-wire or 2-wire plus ground).

In order to have a reliable ground, the ground
construction must be permanent or equivalent.
(Equivalent is taken as by means of industrial-
grade plug and socket schemes.)  1.5.9.4 specifies
the equivalent grounding schemes.

Yes, you are correct in that a VDR is not permitted
to be connected to earth (ground) in pluggable
equipment type A.


Best wishes for a Merry Christmas,
Richard Nute
Product Safety Consultant
San Diego








On 12/14/2010 14:20, Donald McElheran wrote:
> All:
>
> Under clause 1.5.9.4 "Bridging of basic insulation by a VDR" in the
> latest version of 60950-1
>
> Paragraph two:
>
> "Equipment with such a VDR bridging insulation shall be one of the
> following:
>
>       -       equipment that has the provision for a permanently
> connected PROTECTIVE EARTHING CONNECTOR and is provided with
> instructions for the installation of that conductor.
>
>
> This requirement appears to rule out the use of power supplies making
> use of earthed VDRs in their primary circuits, if used in "Pluggable
> Equipment Type A" if a separate earthing terminal is not provided.
>
> Could anyone confirm that this interpretion is correct and wether this
> was the intent of the committee.
>
> Donald McElheran
> Product Compliance Specialist
> Ross Video | Live Production Technology
> www.rossvideo.com
> +1 (613) 652-4886
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to