Scott,

Yes, indeed they do.  In fact with the high voltage applied to 230V 
design centre equipment the result is for it to draw even more power, 
wastefully and expensively, as well as reduce service life.  As an 
example, formerly electric fires could be rated at 240V 3kW, drawing 
12.5A, within the rating of the standard UK 13A domestic socket.  As a 
230V nominal 3kW fire would draw just over 13A at that voltage, and 
even more at the "real" supply voltage of 240V (let alone the 
permitted max of 254V), UK 230V nominal fires now are designed for 
2.75kW instead of 3kW!  

The result of this is to give us substantial business for our energy 
saving voltage regulators, which reduce the supply to a regulated 220V 
or lower.  That is why I gave a reference to the article on our 
website at http://www.claudelyons.co.uk/energy_saving.htm  If you look 
at it, you'll see the title, tellingly, is "Energy Saving and 
Equipment Life Prolongation by Voltage Reduction".  

Apologies if this response is necessarily somewhat commercial, Scott, 
but the argument you give is precisely the rationale for our energy 
saving product line.

Bill

-- 
Bill Lyons - [email protected] / [email protected]


From: Scott Xe <[email protected]>
To: <[email protected]>,
 <[email protected]>
Subject: RE: Domestic mains voltage
List-Post: [email protected]
List-Post: [email protected]
List-Post: [email protected]
Date: Sat, 24 Jan 2009 21:50:16 +0800

Hi Bill,

Thanks for your update on it and useful to understand the direction.

I am unsure if the mains supply companies follow a July 2005 DTI note 
"Electrical Supply Tolerances and Electrical Appliance Safety" points 
out that "Though the electrical supply is quoted as being over a 
range, it is preferable for power distribution companies to keep 
supply voltages as high as possible to minimise current in the supply 
network and hence delaying the need to make improvements in the supply 
infrastructure to increase current handling capability."  Thru recent 
return record and investigation, the domestic mains voltage is at a 
higher side, > or = 250 Vac and the failure return rides up 
significantly.  The manufacturers design their product at EU rated 230 
Vac and assume the product operates at the highest voltage of 254 Vac 
occasionally.  Now, the product is operating at the higher voltages 
all the time.  It results in shortening its life or causing early 
failure.  Luckily this will not happen in other European countries.  

Scott


From: Bill Lyons [mailto:[email protected]] 
Sent: Saturday, January 24, 2009 3:58 PM
To: Scott Xe; [email protected]
Subject: Re: Domestic mains voltage

Scott,

There will be no movement by the UK in the forseeable future.

I append below a definitive response from the UK government's 
Department of Business Enterprise and Regulatory Reform (BERR) to a 
query I made last June.

See also http://www.claudelyons.co.uk/energy_saving.htm

Hope this helps.

Bill

-- 
William Lyons
Claude Lyons Limited, Brook Road, Waltham Cross, Herts EN8 7LR, UK
Direct Tel:  +44 (0)1992 701 500  Mobile: +44 (0)7836 760 372
Switchboard: +44 (0)1992 768 888  Fax:    +44 (0)1992 788 000          
email: [email protected]     URL: http://www.claudelyons.co.uk


From: Scott Xe <[email protected]>
To: <[email protected]>
Subject: Domestic mains voltage
List-Post: [email protected]
List-Post: [email protected]
List-Post: [email protected]
Date: Sat, 24 Jan 2009 13:40:03 +0800

Understand the ultimate goal of nominal mains voltage in EU is 230 Vac 
+/-10%.  Currently, UK is still 230 Vac +10/-6% according to law and 
other EU countries are 230Vac +6/-10%.  Is there any update on the 
progress to the unified tolerance, +/-10%?  

Thanks & regards,

Scott


From: "Wickes Tim (EMU)" <[email protected]>
To: <[email protected]>
Cc: "Enquiry Enquiry (IMSV01)" <[email protected]>; 
 "Scott Giles (EMU)" <[email protected]>
Subject: UK voltage range
List-Post: [email protected]
List-Post: [email protected]
List-Post: [email protected]
Date: 20 June 2008 07:54

Dear Mr Lyons

Low Voltage

The nominal voltage for single phase low voltage distribution in 
Europe is 230V. There is a bandwidth necessary to accommodate load and 
system variants. From 1st January 1995 to present day (from a single 
phase perspective) it is 230V -6%/+10% (216V to 253V) in UK, this 
being the first stage of European Harmonisation implementation). This 
voltage range is a statutory requirement. There is an intention to 
extend this range to 230V +/-10%, i.e. 207V to 253V. This was 
initially scheduled for 1st January 2003 and postponed until 1st 
January 2008. However, there is still some debate amongst stakeholders 
so although some British & European Standards quote 230V +/-10%, and 
information on various internet sites identify 230V +/-10%, the UK 
voltage range will remain at 230V -6%/+10% until further notice. The 
statutory document identifying the range is Electricity Safety, 
Quality and Continuity Regulations (ESQCR) 2002 as amended, s27.  
There will be a trigger for change in this statutory document and this 
will probably be as a result of final agreed consensus (further 
committee work on CENELEC Harmonisation Document 472 and associated 
documents is a likely requirement) of all appropriate stakeholders.  

This range and its proposed staged implementation was agreed via long 
debate in the early 1990's between all stakeholders to accommodate 
both the 240V & 220V ranges used across Europe - the range for the 
220V European stakeholders on 1st Jan 1995 was 230V -10%/+6% (207V to 
244V).  Prior to 1st January 1995 the UK range was 240V +/-6% (i.e. 
226V to 254V). One of the main benefits for voltage harmonisation 
across Europe to 230V nominal has been the standardisation of 
electrical equipment in terms of voltage requirements across the EU, 
providing more choice, improved safety (all European appliances are 
now manufactured to the same voltage standard) and increased 
competition to all. I understand that other countries have also 
standardised to the European nominal 230V (for example, Australia), 
further enhancing competition via standardisation.  

High Voltage

For completeness the bandwidths for High Voltage supplies are as 
follows: High Voltage operating below 132kV +/-6%, High Voltage 
operating at or above 132kV +/-10%.  

I trust this helps.

Regards

Tim Wickes
Energy Markets Unit
Business Enterprise and Regulatory Reform

0207 215 2667


From: Bill Lyons [mailto:[email protected]]
Sent: 19 June 2008 16:08
To: Enquiry Enquiry (IMSV01)
Subject: Voltage range

Dear Sirs,

On page www.berr.gov.uk/energy/reliability/quality-continuity-supply/
your website states that the domestic supply "is set to change to 230
volts +/- 10% (207 to 253 volts) in 2008, this having been postponed
>from 2003."

Please could you confirm this change is to take place and advise the
date on which it is due to occur, and any references to the regulations
mandating it.  

Also, is this change for the UK only, or do you have information on the
dates of implementation in other EU countries, or references to these?

Many thanks

William Lyons

--
William Lyons, Chairman
Claude Lyons Limited, Brook Road, Waltham Cross, Herts EN8 7LR, UK
Direct Tel:  +44 (0)1992 701 500  Mobile: +44 (0)7836 760 372
Switchboard: +44 (0)1992 768 888  Fax:    +44 (0)1992 788 000 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>


Reply via email to