In message 
<[email protected]>, dated 
Tue, 27 Jan 2009, Grace Lin <[email protected]> writes:

>For LISN calibration, what are the calibration standards that I should 
>fill in in the questionaire requested by a calibration lab?  Are ANSI 
>C63.4, CISPR 15, and CISPR 22 appropriate?  These are three test 
>standards I use most.

No, LISN calibration is in CISPR 16-1-2, where they are called 
Artificial Mains Networks (AMNs). See clause 4 and Annex A.

It is a good move to get your LISNs calibrated. Recent experience at a 
test house showed significant differences between supposedly good LISNs.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-