> Ted Eckert wrote: > > ... you will > still be required to prove that the product is safe on that > 30 A circuit. That means that wires either need to be sized > for 30 A or you have to pass the tests in 60950-1 section > 2.6.4.3.
The above is the key. If the product has wire sized for 30 A and is adequately protected internally to accept the faults available from a 30 A branch, that should be adequate to meet the needs of safety. I'm not aware of any Code based requirement claiming only loads between 16 A and 24 A can be on a 30 A circuit. If you can find one, I'd appreciate the reference. BTW, 15 A breakers are a standard size and is identified as such in my 1999 NEC, ยง240-6. The Code, on the other hand, allows any NEMA 5P device to be protected by a 20 A breaker. Peter Tarver - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]> All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc Graphics (in well-used formats), large files, etc. can be posted to that URL. Website: http://www.ieee-pses.org/ Instructions: http://listserv.ieee.org/request/user-guide.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <[email protected]> Mike Cantwell <[email protected]> For policy questions, send mail to: Jim Bacher: <[email protected]> David Heald: <[email protected]>