> Ted Eckert wrote:
> 
> ... you will
> still be required to prove that the product is safe on that
> 30 A circuit. That means that wires either need to be sized
> for 30 A or you have to pass the tests in 60950-1 section
> 2.6.4.3.

The above is the key.  If the product has wire sized for 30 
A and is adequately protected internally to accept the 
faults available from a 30 A branch, that should be 
adequate to meet the needs of safety.

I'm not aware of any Code based requirement claiming only 
loads between 16 A and 24 A can be on a 30 A circuit.  If 
you can find one, I'd appreciate the reference.

BTW, 15 A breakers are a standard size and is identified as 
such in my 1999 NEC, ยง240-6.  The Code, on the other hand, 
allows any NEMA 5P device to be protected by a 20 A 
breaker.