RJ connectors are suitable for residential and office when used within the
conditions of acceptability that would conform to NEC. And my furry
friends chew all available Cat 5 stuff with no obvious effects, other than
excessive salivation.

Did not want to bring this up, but here I go into the abyss. IMO, 1863 has
some problems for your defined end-use because:

- the probe in fig 8.1 does not conform to accessibility requirements in
NEC for hazardous voltages
- the scope disallows conformance with article 800
- definition of hazardous V and energy and VA does not conform to article
725 or UL1310.
- the current protection tests are for a phone system/CO, but the scope
disallows most telephone equipment
- the standard does not address all user protection requirements as the
standard is generally intended for professional equipment that is not
accessible

etc, etc, etc

R/S,
Brian 

 > -----Original Message-----
 > From: Ilan Cohen [mailto:[email protected]]
 > Sent: Wednesday, May 26, 2010 9:57 PM
 > To: Brian O'Connell; [email protected]
 > Subject: RE: PoE which is not power limited.
 > 
 > Hi Brian
 > 
 > In your comments you say that you do not think RJ connecters are
 > suitable for Home usage. Where do you get that from? 
 > 
 > RJ45 is commonly used in the home and as long as they are UL1863 they
 > are considered to be safe.
 > 
 >  Ilan Cohen, Technical Director
 > 
 > -----Original Message-----
 > From: [email protected] [mailto:[email protected]] On Behalf Of Brian
 > O'Connell
 > Sent: Wednesday, May 26, 2010 6:52 PM
 > To: [email protected]
 > Subject: RE: PoE which is not power limited.
 > 
 > Dear y'all (strange, I do not remember meeting any rednecks 
 > in Israel)
 > 
 > Read and heed the advice of Mr Eckert - his MS job has 
 > probably resulted
 > in much experience with the physical layer of TCP/IP. To 
 > expand on his
 > comments - read article 725 before you decide to use Class 2 wiring
 > materials.
 > 
 > A good reference for these questions is probably Peter 
 > Tarver - perhaps
 > he
 > will respond.
 > 
 > 1. Cat 5e cable is defined by TIA-568-B. The connector is defined by
 > TIA-1096-A. The UL-recognized material that I have used is rated 120V
 > WV,
 > 1.5A, and 1500V di-electric withstand - so the wiring stuff is
 > available.
 > Unfortunately, I have not found any suitably-rated plastic 
 > patch panels
 > -
 > so use metal construction to mount the stuff.
 > 2. Depends if exits building, max overload current and VA available,
 > reference of a local protective earth, and the ratings and C of A for
 > the
 > power source.
 > 3. Do not understand the need for a "new definition", see 
 > 2.6 and 6.2 of
 > 60950-1 and section 6 of 60950-21. SELV and TNV-1 do not meet all
 > requirements for use of Class 2 wiring materials.
 > 
 > In addition to electrical code issues, you will find that the RJ
 > connectors are not suitable for construction that is exposed to
 > home-user/installer.
 > 
 > Brian 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to