Hi Brian,

 

To answer your question, look at clause 1.7.8.1 of IEC 60950-1:

“Unless it is obviously unnecessary, indicators, switches and other controls 
affecting safety shall be identified or located so as to indicate clearly which 
function they control. Markings and indications for switches and other controls 
shall be located either:

− on or adjacent to the switch or control, or

− elsewhere, provided that it is obvious to which switch or control the marking 
applies.

Indications used for this purpose shall, wherever practicable, be 
comprehensible without a knowledge of languages, national standards, etc.”

 

As I am not familiar with IEC/EN 61010-1, does it have the same or similar 
requirement wording? Regardless, if any of the circuit breaker/switches serve 
as safety disconnect devices, then they must be so identified, as I’m sure that 
you’re already aware. The disconnect device ID’s should be clearly stated or 
the main disconnect could be of a different color than the rest, if that’s 
possible (not sure how that would benefit color blind folks). This is in 
addition to the | and O dilemma you were inquiring about.

 

Anyway, IHTH.

 

Best regards,

 

Ron

 

From: Kunde, Brian [mailto:[email protected]] 
Sent: Thursday, February 25, 2010 8:34 AM
To: [email protected]
Subject: Re: [PSES] Use of | and O symbols

 

Thanks to all who replied to my email. I was expecting reassurance that my 
understanding of this topic, going back some 25 years, still holds true. But 
once again, it appears as if things are changing without my knowledge which 
really makes for a bad day. I really hate it when I have to tell engineering I 
was wrong.

 

Though it appears that using the |/O symbols on switches other than the 
disconnect device is a violation of IEC/EN 61010-1 Ed. 2, other standards seem 
to contradicts this. Does anyone have a pre-release version of the IEC 61010-1 
Ed. 3 to see what it says on this topic?

 

The IEC 60934 standard for Circuit Breaker (including those with switches) 
states that the switch must be marked with the |/O symbols. It says nothing 
about disconnect device. "For CBEs other than those operated by means of 
push-buttons, the open position shall be indicated by the symbol "O" and the 
closed position by the symbol "I" (a short vertical straight line).” This is 
why our circuit breaker vendor is saying our breakers must have the |/O symbols 
regardless of their use. 

 

The following UL60950 Guideline document recommends using the |/O symbols on 
ALL switches to show the On/Off position. (thanks to Sylvia for sending this to 
me)

 

http://data.ul.com/pagos/access/60950/1783003.asp

 

“UL60950: Per 3.4.8, switches and controls which are considered the main 
disconnect device shall be marked "|"/"O". Also, if a switch is located in the 
primary and it affects safety, e.g. it controls hazardous moving part, it shall 
be marked "|"/"O". Other switches which do not affect safety, including primary 
and secondary controls, do not need to be marked "|"/"O", although this is the 
preferred method of indicating on and off positions.”

 

So if the |/O symbols can be used on switches other than the Disconnect Device, 
then how are you to identify the Disconnect Device?  Is there an international 
symbol for Disconnect Device? If not, maybe there should be.

 

Thanks again to all.

The Other Brian

 

________________________________

From: [email protected] [mailto:[email protected]] On Behalf Of Kunde, Brian
Sent: Wednesday, February 24, 2010 1:06 PM
To: emc-pstc
Subject: Use of | and O symbols

 

Reference IEC/EN 61010-1 2nd Ed. Safety Standard. Our product is considered 
Laboratory Equipment.

 

The | and O symbols are on our Mains Supply Switch/Breaker which is also our 
Disconnect Device, but engineering wants to use additional switch/breakers 
(functional purpose) to power on/off different sections of the product.  The 
switch/breakers they want to use are breaking AC Mains to sections of the 
product and have the  | and O symbols printed right on the switches.

 

It has always been my understanding that the | and O symbols can only be used 
on the Disconnect Device which cuts AC mains to the entire product.

 

Can the | and O symbol also be used on other AC Main switch/breakers that cut 
AC Mains Supply power to only sections within the product but not the entire 
product?  

 

In our case, these additional switch/breaker cut AC mains to circuits but there 
are other circuits in the same section that are still powered up.  The purpose 
of these additional switches are to power down sections or devices for power 
savings at night when some sections of the product need to stay on 24/7.

 

One last detail; all the switch/breaker including the Disconnect Device switch 
are all physically mounted on the same panel right next to each other, so I am 
concern with the proper identification of the Disconnect Device switch.

 

Other than the | and O symbol, are there other ways to identify the Disconnect 
Device switch?

 

The manufacturer of the switch/breakers will not make it without the | and O 
symbols without loosing its VDE certification. 

 

I’ve been telling engineering that the | and O symbols can only be used on the 
Disconnect Device. Am I wrong?  

 

The standard says, “Symbols | and O shall not be used for switches other than 
the power supply switch.”, however, section 5.1.6 says, “If the power supply 
switch .. is used as the disconnecting device…”, implies that a power supply 
switch does not have to be the Disconnect Device.  

 

Please help clarify this circular logic for me.

 

The Other Brian

 

PS:  Here is the entire section 5.1.6 to use as a referrence:

 

5.1.6 Switches and circuit-breakers

If the power supply switch or circuit-breaker is used as the disconnecting 
device, the on-position

or the off-position shall be clearly marked. Symbols 9 and 10 of table 1 can, 
in some

cases, also be suitable as the device identification (see 6.11.2.5). A lamp 
alone is not

considered to be a satisfactory marking. Symbols 9 and 10 shall not be used for 
switches

other than the power supply switch.

 

6.11.3.1 Switches and circuit-breakers

An equipment switch or circuit-breaker employed as a disconnecting device shall 
meet the

relevant requirements of IEC 60947-1 and IEC 60947-3 and be suitable for the 
application.

If a switch or a circuit-breaker is used as a disconnecting device, it shall be 
marked to

indicate this function. If there is only one device – one switch or one 
circuit-breaker – symbols

9 and 10 of table 1 are sufficient.

A switch shall not be incorporated in a MAINS supply cord.

A switch or circuit-breaker shall not interrupt a protective earth conductor.

A switch or circuit-breaker with contacts for disconnecting and other contacts 
for other

purposes shall conform to the requirements of 6.6 and 6.7 for separation 
between circuits.

Conformity is checked by inspection.

 

 

 

 

 

_________________________ 

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you. 

_________________________ 

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you. 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at 
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at 
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to