When I worked for a contractor building a hydroelectric dam for the Army Corps
of Engineers (a long time ago) we tested the insulation on motors with a 1000
V megger.  The spec called for at least 1 MOhm resistance, but we typically
saw the meter read infinity.  And we tested each motor as it was installed,
along with all the wiring in the dam.  Not exactly the most entertaining part
of a summer job I had, arguing with the CoE electrical inspector about how to
do it (he had his idea, their written specification had another) was a lot
more fun.  J

 

Ghery Pettit

 

 

From: [email protected] [mailto:[email protected]] On Behalf Of ce-test,
qualified testing bv - Gert Gremmen
Sent: Thursday, November 19, 2009 2:54 AM
To: [email protected]
Subject: Dielectrical tests for motors

 

Anyone out there that my shine some light on dielectrical withstand tests for
squirrelmotors ?

as a component ??

Motor  1 kW  400 Vac 3-phase

 

CSA 22.2  Class 4211 01  / 4211 81

 

There is some problems here with a manufacturer

claiming its product was type tested with 600 Vac and 1 second.

 

 

 

Regards,

Ing. Gert Gremmen

 

[email protected]

www.cetest.nl


Kiotoweg 363

3047 BG Rotterdam

T 31(0)104152426
F 31(0)104154953

 

 Before printing, think about the environment. 

 

 

Van: [email protected] [mailto:[email protected]] Namens Haynes, Tim (SELEX
GALILEO, UK)
Verzonden: Thursday, November 19, 2009 11:27 AM
Aan: [email protected]; Amund Westin; [email protected]
Onderwerp: RE: IP test - pass or fail?

 

Hi All,

 

I might have too much sawdust between the ears but Armud said, in the original
e-mail, that the test is IPx6 and then mentioned drain holes.

 

Would drain holes be expected in an IPx6 (waterproof) enclosure? I would have
thought that the “waterproof” requirement was incompatible with the
fitting of drain holes !?

 

Is this the problem?

 

Regards

Tim

 

************************

Tim Haynes A1N10

Electromagnetic Engineering Specialist

SELEX Sensors and Airborne Systems 

300 Capability Green

Luton LU1 3PG

( Tel      : +44 (0)1582 886239

7 Fax     : +44 (0)1582 795863

) Mob    : +44 (0)7703 559 310

* E-mail : [email protected]

P Please consider the environment before printing this email. 

 

There are 10 types of people in the world-those who understand binary and
those who don't. J. Paxman

________________________________

From: [email protected] [mailto:[email protected]] On Behalf Of Don Gies
Sent: 18 November 2009 21:45
To: 'Amund Westin'; [email protected]
Subject: RE: IP test - pass or fail?

 

Hello Amund,

 

Generally, if you have chosen to make an enclosure IPX6 for whatever reason,
you probably have a robust system of gaskets and enclosure, and truly expect
no water inside the enclosure.  The fact that you had a little bit of water
penetrating an IPX6 enclosure is normally an indication that that robust
system of gaskets and enclosure suffered a near-miss failure.  At this point,
you would either have the mechanical designers make re-adjustments (adjust the
torque values of fasteners, bring in the paw latches on doors, use a thicker
gasket, etc.), or you would re-test at a less-severe enclosure value such as
IPX5, if that is an option.

 

Another concern is whether the water came in to a “wet area”, one equipped
with drains that you expect to get wet, or did it penetrate the enclosure in a
random manner and get on top of electronic parts that expect to be in a dry
location.   If it came in randomly, say in the middle of a gasketed-door
interface, then you probably want to reject these results, modify and retest.

 

I have in-house capability to test for IPX6 as well as NEMA 4, and I get
designers to send me test samples early.  This is  because, from a probability
standpoint, I expect them to fail more times than not the first time through. 
There is a normal test-mitigate-retest progression that goes on.  Water
ingress failures tend to be chaotic in nature, and are often difficult to fix.
 So, early testing allows the designer time to make changes.

 

One last point—the “garden-hose test” that you might have conducted on
your sample before subjecting it to the IPX6 test is fine to weed out obvious
problems, but it is not in the class of water impact that the IPX6 test
delivers at 100 liters per minute through a 12.5 mm diameter nozzle.  It is
closer to pre-compliance for an IPX5 test of 12.5 liters per minute through a
6.3 mm diameter nozzle.

 

Best regards,

 

Don Gies

Senior Product Compliance Engineer

Alcatel-Lucent

Murray Hill, NJ  07974-0636 USA

 

 

________________________________

From: Amund Westin [mailto:[email protected]] 
Sent: Wednesday, November 18, 2009 11:37 AM
To: [email protected]
Subject: IP test - pass or fail?

 

We’re doing an IPX6 test (high pressure water jet) according to IEC60529.

 

Some water enter the unit, but drain holes make their job. Only plastic
enclose in that area anyway.

But, a few drops are discovered on a plastic material switch inside the unit
and also some drops on two connection poles on the swicth. 

 

We have failed on this test because (according to the test lab) in the long
term, creepage currents can cause the two poles to be shorted and thereafter a
incorrect function will appear. 

 

Is it likely to believe that such creepage currents can occur, when the two
poles are placed 10mm from each other and the voltage supply is 3.3VDC?

 

b.r.

Amund

 

 

SELEX Sensors and Airborne Systems Limited
Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex SS14
3EL
A company registered in England & Wales.  Company no. 02426132
********************************************************************
This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.
********************************************************************

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to