Definetly use an approved PTC.  The testing is long term and follow up
services in proving the same PTC is used that was tested will get messy.
You will likely also be required to do a temperature test with
thermocouples on surfaces near the PTC.  They do tend to get hot when
performing their function.

John Allen

Product Safety Consulting, Inc.

605 Country Club Dr. | Stes. I & J | Bensenville, IL 60106

630-238-0188 | 800-233-7738 | 630-238-0269 (f)

[email protected]

www.productsafetyinc.com 



Although PSC maintains the highest level of virus protection, this
e-mail and any attachments should be scanned by your virus protection
software.  It is the responsibility of the recipient to check that it is
virus free.  PSC does not accept any responsibility for data loss or
systems damage arising in any way from its use.  This message is
confidential and intended only for the individual to whom or entity to
which it is addressed.  If you are not the intended recipient or
addressee, or an employee or agent responsible for delivering this
message to the addressee, you are hereby notified that any
dissemination, distribution, or copying, in whole or part, of this
message is strictly prohibited.  If you believe that you have been sent
this message in error, please do not read it.  Please immediately reply
to sender that you have received this message in error.  Then
permanently delete all copies of the message. Thank you. 




From: Greg McClure [mailto:[email protected]] 
Sent: Wednesday, November 18, 2009 11:41 AM
To: [email protected]
Subject: Re: [PSES] PTC Test Requirements


Brian,

You can easily avoid being concerned with the details of the test. When
you choose the PTC for your design, make sure you pick one that already
has component recognition/approval to IEC 60730-1. You will find that
many of them have UL and TUV component approval already. The PTC vendors
typically show the test mark approvals on their data sheets. You then
can request a copy of the certificate from the PTC manufacturer to
verify that it is to the proper version and clause(s) of the standard.

By using the recognized component, you avoid the component testing and
conditioning required in 60730-1. You may still have to perform testing
on the I/O pin to prove your design meets requirements at the connector
but that is much easier than the component level test.

Regards,

Gregory H. McClure
Lexmark Product Safety
859 232 3240 office
859 232 6882 fax

Confidentiality Notice:
This e-mail message, including any attachment, is for the sole use of
the intended recipient(s) and may contain confidential information. Any
unauthorized review, use, disclosure or distribution is strictly
prohibited. If you are not the intended recipient, please contact the
sender, by e-mail, and destroy all copies of the original message.



 

             "Kunde, Brian"

             <brian_kunde@LECO

             TC.COM>
To 
             Sent by:                  <[email protected]>

             [email protected]
cc 
 

 
Subject 
             11/18/2009 11:36          PTC Test Requirements

             AM

 

 

 

 

 





According to IEC/EN 60950 section 2.5b, a positive temperature
coefficient device (PTC) can be used to limit current for a limited
power source circuit.

It says the PTC has to "pass the test specified in IEC 60730-1, clauses
15, 17, J.15 and J.17".  I don't have this standard. Can someone outline
the test requirements for me? I'm trying to avoid adding another
standard to our library unless we really need to.

Application:  Sometimes we would like to supply 24Vdc to an I/O port to
operate a device outside the fire enclosure. I assume a PTC or Pico Fuse
can be used for this application. We drive the I/O circuit with a
programmable High-Side Driver programmed to 4 amps max but someone
suggested that we cannot rely on it for safety in this application. Any
other suggestions?

Thanks to all,
The Other Brian


_________________________

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received
this by mistake, please destroy it and notify us of the error. Thank
you.
-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to < [email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.


Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html


For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>


For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to