One of the good people of the PSTC community had recently sent me an off-line
question about North American requirements for stuff connected to a computer
port. And I cannot remember whom...

The following is from the CSDS Proposal for UL1310, published today (26Oct):

"78.2.2 – Since the ITE derived source may, under normal and single fault
conditions, have LPS capacity, the power unit must be designed to withstand
any input within the LPS range (limits of 60 Vdc, 100 VA, 8 A)."

Please note that these limits, while they may define a limited power source
within the meaning of UL/CSA60950-1, they do NOT necessarily meet requirements
for an inherently limited Class 2 source as required by NFPA for "Class 2 not
wet/Class 3 wet". There are other requirements for control/power lines.

So the answer to your question would be no direct connection, and that you
would still need to use a recognized component PTC.