Think 50/60Hz -> X = 2*pi*f*L and the other 'X' for the representative freq
for that step response -> think about Q = X/R for principle freqs.

Think about capacitance between windings for a very hi-V step response.

Think about what the L in ground may do to conducted emissions for the power
supply.

Think about the ground bond test in CSA 0.4, and performance requirements in
NFPA 70. And if you are really really worried about the big surge, look at FAA
019E and NFPA 780.

FWIW, recently did a 5000VA device with this construction - no problems, but
the choke used 12ga wire and huge ground straps.

Brian 


From: [email protected] [mailto:[email protected]]On Behalf Of Dean Gerard
(Medical Physics)
Sent: Thursday, October 15, 2009 3:53 AM
To: [email protected]
Subject: inductive filter in PEC

I'd be grateful for people's views on the wisdom of including an inductive
filter (for fast transient suppression) in the protective earth conductor of a
device.

Since safety in the event of a fault to earth relies. in most installations.
upon automatic disconnection of supply, which in turn relies upon
low-impedance earth-fault loop, does the inclusion of an inductance in this
loop not then compromise this safety feature by potentially increasing
disconnection time in the event of such a fault?  (the shock hazard being a
function of duration as well as magnitude)

Furthermore, that part of earth-loop impedance attributable to the device,
rather than the installation, is tested by DC earth bond resistance
measurement.  How valid a measure is this with an inductance present, since
the earth-fault will not be DC but at mains frequency and typically generated
as a transient step-type function when the fault occurs (to which the
inductance will present a much higher impedance).

Thanks
Ged Dean

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to