In IEC 61000-4-11:2004 above Table 1, is the vague phrase:
"Shorter durations in the table, in particular the half-cycle, should be 
tested to be sure that the equipment under test operates . . . "

Testing may have shown that some mains transformers have problems with 
successive half-sines of the same polarity.  For example,  ' + - + _ + - 
+'  (the underscore is a half-cycle dropout at 180 degrees.)

Pat Lawler
EMC Engineer
SL Power Electronics Corp.

[email protected] wrote on 09/17/2009 01:36:42 PM:
> I believe the change is to reflect alignment with the base 
> dips/interruptions spec EN/IEC 61000-4-11:2004 Table 1 . "Preferred 
> test level and  durations for voltage dips", Class 2, which has both
> 1/2 and 1  cycle 0% dips. 
>  
> See EN 300 386 v1.4.1 Section 2.1 Normative References [14]. The 
> previous  EN 300386 v1.3.2 cited an undated reference for 
> 61000-4-11, but the new one is a  dated reference (2004).
>  
> William T.  Sykes
> Compliance  Engineer
> Motorola Home &  Networks Mobility
> 101 Tournament  Drive
> Horsham, PA  19044
> 215-323-2619
> [email protected] 
> 
> From: [email protected]  [mailto:[email protected]] On Behalf Of Monrad 
Monsen
> Sent: Thursday, September 17, 2009 3:08 PM
> To: [email protected]
> Subject: Clarification on ETSI EN 300 386  v1.4.1
> 
> I need help in understanding ETSI EN 300 386 v1.4.1 (2008-04).   In 
> section 7.2.2.4 (page 26) for "Other than telecommunication centres,
> AC power  ports", the standard gives the requirement for a "voltage 
> dips and short  interruptions immunity test" (7.2.2.4.4) stating 
thefollowing:
>            Residual voltage  %              
> 0                           Criteria  B
>                    Cycle                    0.5
>           Residual  voltage  %              
> 0                           Criteria  B
>                    Cycle                    1
> 
> Both have the same performance criteria requirement (Criteria B) 
> and both are full voltage interruptions (0%), so the two entries are
> redundant.  Obviously, this is a typographical error.  We just need 
> to  know which is the actual requirement of the standard.  Either 
> the standard  wants us to test for a half cycle (10 ms) or for a 
> full cycle (20 ms).
> 
> In  the earlier revision (ETSI EN 300 386 v1.1.3), section 7.2.2.4 
> required the  following voltage interruption  test:
>           Voltage  reduction  %              
> >95                           Criteria  B
>                    Duration ms                 10
> 
> Did ETSI EN 300 386 v1.4.1 intend to keep the same duration using 
> 0.5 cycle (same as 10ms from the past) so the other entry is the 
> actual error,  or did the committee really want to increase the 
> required voltage interruption  immunity by testing a full 1.0 cycle 
> (doubles the requirement to 20ms) so the  first entry is really the 
error?
> 
> Note:  ETSI EN 300 386 v1.4.1 is  titled "Electromagnetic 
> compatibility and Radio Spectrum Matters (ERM);  Telecommunication 
> network equipment; ElectroMagnetic Compatibility (EMC) 
> requirements."  The date of withdrawal (dow) or date when this 
> standard  revision becomes mandatory in Europe is 31 July 2011.
> 
> Thank you. 
> -- 
> 
> Monrad  L. Monsen
> Worldwide Compliance  Officer
> Sun  Microsystems
> [email protected]
> 303.272.9612  Office
> 
>   
> 
> -
> ----------------------------------------------------------------
> This  message is from the IEEE Product Safety Engineering Society 
> emc-pstc discussion  list. To post a message to the list, send your 
> e-mail to <[email protected]>
> 
> All emc-pstc  postings are archived and searchable on the web at 
> http://www.ieeecommunities.org/emc-pstc
> Graphics  (in well-used formats), large files, etc. can be posted to
> that URL. 
> 
> Website: http://www.ieee-pses.org/
> Instructions:  http://listserv.ieee.org/request/user-guide.html
> List  rules: http://www.ieee-pses.org/listrules.html 
> 
> For help, send mail to the list administrators:
> Scott Douglas <[email protected]>
> Mike Cantwell  <[email protected]> 
> 
> For policy questions, send mail to:
> Jim Bacher <[email protected]>
> David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to