My point is that the NEC tries to minimize the risk to the electrical system
and its components from lightning. It is NOT designed to protect the building
>from lightning. You really must go to other standards for that.
Use NFPA 780 and UL 96A, and UL's Lightning Protection Systems
<http://www.ul.com/global/eng/pages/off
rings/services/globalfieldservices/fieldservices/lightningprotection/> 
installation certificate program.

Bob Johnson

Grasso, Charles wrote: 

        Hi Bob,

         

        The typical lightning protection the NEC code requires is exactly what 
Derek
is concerned about!

         

        I am not sure whether not the NEC code covers metallic buildings. 
Perhaps
this is the first place
        to start.

         

        Chas

         

         

        
________________________________


        From: [email protected] [mailto:[email protected]] On Behalf Of Robert 
Johnson
        Sent: Monday, August 31, 2009 8:58 AM
        To: [email protected]
        Subject: Re: Thoughts and opinions sought]

         

        
        Your building needs two things:
        - a good lightning protection system (you know, with lightning rods).
        - a good electrical system.
        >From what I have seen, you are trying to make your building lightning
protected by building a good electrical system.
        
        I have no confidence in my ability to design lightning protection and 
have
not seen any comments or replies yet which properly address it. It will not
rely on siding or screws, etc. Trust a good contractor to install a good (UL
Listed - they actually approve the building) lightning protection system. The
standards for lightning protection (not meaning the electrical code) have been
well thought through and will do a good job. As part of this they will install
proper earth electrodes and building bonding.
        
        The electrical system grounding is meant to provide an equipotential
environment which will handle system ground faults and shock risk. As part of
that equipotential setting, the bonding to the building and to the lightning
ground path is described in the code. The code goes to great lengths to assure
this equipotential environment. The dirt connections assures you don't get
into trouble when you stand outside in the wet dirt and touch the metal
building. The ground electrodes have essentially nothing to do with the
interior environment.
        
        I think the reason you are feeling unsure is that you have been trying 
to use
the electrical code for lightning protection. It was not designed for that and
your guesses at improvements will at best be uncertain and likely inadequate.
        
        Bob Johnson
        ITE Safety <http://www.itesafety.com> 
        
        Derek Walton wrote: 

        Morning all, 
        
        I'm pondering which path to follow with a grounding issue. I'm not so 
much
concerned with code requirements, I see these as the minimum, I'm after
best... 
        
        First some background. I have built a building to house my business. 
I've
located this well in the boonies on some 23 acres of woods. In order to blend
in it's in the shape of a classic Midwest USA barn. It was custom engineered
>from Steel red-iron and Steel siding. 
        
        My quandary is how best to ground this for electrical safety and 
lightning.
It's a fairly large building ( 50 feet by 80 feet ) and reaches almost to the
tops of surrounding trees. Terrain wise we seem to have a fair number of
strikes, in the last 5 years we have lost 3 trees to lightning. 
        
        If I follow guidance I have been given to ground the building only 
where the
power enters, I see this as a week point during a lightning event. 
        
        A bit more about the building. If you can imagine 5 huge horseshoes 
stood
upright on the open end, thats what the main frame looks like. There is of
course a large amount of interconnecting red iron and two additional vertical
columns at each end of the building. Over the whole frame is steel siding. The
whole thing is bolted together with many 1 inch and 1/2 inch bolts. The siding
has close to 8000 screws fastening it to red iron. 
        
        The building stands right now about 1 foot above "dirt" on a concrete 
footing
wall, and there is a 10 foot wide concrete path to be installed all around the
building making up the 1 foot height difference: the solution to my quandary
is needed before the concrete can be installed. Soon would be nice so I can
quit getting muddy boots :-) 
        
        I'm leaning towards installing a copper grounding ring all around the
building say 4 to 5 feet or maybe up to 10 feet away from the footing wall.
This ring will be about a foot down in the dirt. At the point where each
building column touches the concrete I'm looking to install a heavy ( 4/0 )
grounding wire out to the wire ring. At the point they meet I'll drive a 10
foot grounding rod flush with the wire ring and join them with exothermic
welds. 4/0 wire is easy to get here, but copper strips may also be an option. 
        
        I'm looking for thoughts, opinion, recommendations on whether this 
approach
is sound, sufficient, overkill, under kill etc. Both I, and my boots, would
appreciate the groups thoughts. 
        
        Sincerely, 
        
        Derek Walton 
        L F Research 
        
        - 
        ---------------------------------------------------------------- 
        This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]> <mailto:[email protected]>  
        
        All emc-pstc postings are archived and searchable on the web at: 
        http://www.ieeecommunities.org/emc-pstc 
        Graphics (in well-used formats), large files, etc. can be posted to 
that URL. 
        
        Website:  http://www.ieee-pses.org/ 
        Instructions:  http://listserv.ieee.org/request/user-guide.html 
        List rules: http://www.ieee-pses.org/listrules.html 
        
        For help, send mail to the list administrators: 
        Scott Douglas <[email protected]> <mailto:[email protected]>  
        Mike Cantwell <[email protected]> <mailto:[email protected]>  
        
        For policy questions, send mail to: 
        Jim Bacher:  <[email protected]> <mailto:[email protected]>  
        David Heald: <[email protected]> <mailto:[email protected]>  
        
        

        -
        ----------------------------------------------------------------
        This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>
        
        All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
        Graphics (in well-used formats), large files, etc. can be posted to 
that URL. 

        Website: http://www.ieee-pses.org/
        Instructions: http://listserv.ieee.org/request/user-guide.html
        List rules: http://www.ieee-pses.org/listrules.html 

        For help, send mail to the list administrators:
        Scott Douglas <[email protected]>
        Mike Cantwell <[email protected]> 

        For policy questions, send mail to:
        Jim Bacher <[email protected]>
        David Heald <[email protected]> 

        -
        ----------------------------------------------------------------
        This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>
        
        All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
        Graphics (in well-used formats), large files, etc. can be posted to 
that URL. 

        Website: http://www.ieee-pses.org/
        Instructions: http://listserv.ieee.org/request/user-guide.html
        List rules: http://www.ieee-pses.org/listrules.html 

        For help, send mail to the list administrators:
        Scott Douglas <[email protected]>
        Mike Cantwell <[email protected]> 

        For policy questions, send mail to:
        Jim Bacher <[email protected]>
        David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to