I wonder if it’s significant that IEC 61140 refers to ELV (no provision for
fault protection). Note 2 below indicates that ELV is only accepted for
connection to SELV or PELV. What voltage limits does IEC 60254-4-41 give for
SELV and PELV? IEC 60204-1 gives the DC limit for PELV at 60Vdc ripple-free
for dry locations where large area contact with a human body is not expected.
IEC 60950-1 gives 60Vdc as the limit for SELV under normal operating
conditions (no fault). Without having copies of these standards (IEC 61140 or
IEC 60254-4-41), I would guess that ELV is not allowed to be accessible, only
SELV or PELV.

 

IEC 61010-1 does not consider DC voltages up to 140Vdc as Hazardous Live for a
single fault in dry conditions.

 

IEC 60950-1 also allows DC voltages up to 120Vdc on SELV circuits after a
single fault for a defined limited duration or limited duty cycle.

 

Scott Aldous

Compliance Engineer

Advanced Energy

Tel: 970-407-6872

Fax: 970-407-5872

________________________________

From: [email protected] [mailto:[email protected]] On Behalf Of Charlie
Blackham
Sent: Thursday, July 30, 2009 9:14 AM
To: [email protected]; [email protected]
Subject: RE: [PSES] "safe" voltage differences between UL 1703 and IEC 61140

 

Class III equipment shall be designed to be supplied at voltages up to 120V,
and that it must be connected to a SELV or PELV circuit. 

 

ELV levels depend on the environmental conditions of the skin – immersed,
wet or dry, with DC limits in IEC61201 of 0V, 35V and 70 V respectively. This
DC limit may be higher for charging batteries.

 

I don’t have a copy of UL 1703, but assuming Photovoltaic cells are designed
to be installed outdoors (!), a maximum contact voltage of 30V dc, is the same
as that for outdoor IT equipment in 60950-22, and not far off the 61201 ELV
limit for “Wet” skin or 35V

 

Regards

Charlie

 

 

From: Lauren Crane [mailto:[email protected]] 
Sent: 30 July 2009 15:18
To: [email protected]
Subject: [PSES] "safe" voltage differences between UL 1703 and IEC 61140

 


A colleague has stumped me with the following question. 

================== 
A supplier of a Photovoltaic panel cited IEC 61140 (Protection against
electric shock – Common aspects for installation and equipment)  as
referencing a "safe" voltage to be as high as 120 Vdc.   This is puzzling
because UL 1703 (Flat-Plate Photovoltaic Modules and Panels) appears to define
the electric shock threshold at 30 Vdc.   How can electric shock threshold for
UL 1703  be set at 30 Vdc, but IEC 61140 considers the upper "safe" limit to
be 120 Vd.c.? 

***************************************
***********************************************************************
IEC 61140 - Protection against electrical shock - common aspects for
installation and equipment 
Section 7.4 Class III Equipment 
Equipment relying on limitation of voltage to ELV values as provision for
basic protection and with no provision for fault protection. 
7.4.1 Voltages 
7.4.1.1 Equipment shall be designed for a maximum nominal voltage not
exceeding 50V a.c. or 120 V d.c. ripple free. 
... 
NOTE 2: According to clause 411 of IEC 60264-4-41, class III equipment is
accepted only for connection to SELV and PELV systems. 
***************************************
************************************************************************* 

Any ideas on the rational behind this difference? 

Regards, 
Lauren Crane 
Product Regulatory Analyst
Corporate Product EHS Lead
Applied Materials Inc.
Austin, TX 512 272-6540 [#922 26540]

- external use -

Save paper and trees!  Please consider the environment before printing this
e-mail. 

This message, including any attachments, may contain information that is
confidential and proprietary information of Advanced Energy Industries, Inc.
The dissemination, distribution, use or copying of this message or any of its
attachments is strictly prohibited without the express written consent of
Advanced Energy Industries, Inc. 
-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to