Table 13.5, Note 2 - The sources for the ampacities in this table are Table
310-16 of NFPA 70, National Electrical Code.

My _conjecture_ is that it will correspond to the 25% de-rate that is used for
the self-heating for several conductors in a raceway.

Brian
 

From: [email protected] [mailto:[email protected]]On Behalf Of
[email protected]
Sent: Monday, July 20, 2009 12:35 PM
To: 'IEEE EMC & SAFETY PSTC'
Subject: NFPA 79 2007 section 19.3 - why 125%

Does anyone know why NFPA 79 requires servo system conductors to be sized to
125% of the [servo] equipment? What is foreseen in a servo system's current
profile that warrants the extra "head room?" 

Regards, 
Lauren Crane 

-