did not see any replies, so here we go...

1. inspector viewpoint -> UL61010-1 states conformity to the standard =
NEC conformity - the device has NOT been tested to UL61010-1, so no
presumption of NFPA conformity can be assumed.
2. in general, if xfmr outputs are accessible or not insulated, then the
transformer should be inherently limited per Class 2/3 requirements (see
UL5085-3), or all outputs shall be protected.
3. EN/UL61010-1 has specific overload and short tests for all secondary
windings of xfmrs connected to mains. The fuse is NOT in the circuit
during the O/L test, so the xfmer must have some limiting impedance built
in to pass this test.
4. the 9A CB in the input can only be depended for protection (that is,
used during Type Tests) of equipment if it is permanently connected.
otherwise, assume 20A input.
5. if all xfmrs are inherently limited, i.e., certified as a fail-safe
according to IEC61558-2-6 and/or Class 2/3 inherently limited according to
UL5085-3, and if proper materials for input wiring are used, input ckt of
unit should conform to NEC.
6. NFPA70 Table 450.3 is scoped for building equipment, i.e., a
distribution xfmr that forms the input to a branch ckt. your box is
connected to a branch ckt - WHY IS THE INSPECTOR NOT USING ARTICLE 725 ?? 

do not feel alone - i get similar stupidity from 'inspectors' that audit
the end-use boxes that my customers build. is there a fire marshal lurking
that can comment on this ??


 

From: [email protected] [mailto:[email protected]]On Behalf Of Kunde,
Brian
Sent: Friday, May 22, 2009 7:01 AM
To: [email protected]
Subject: Protecting Transformers and the NEC

Greetings Experts. I need some understanding regarding properly protecting
a transformer (according to the 610101-1) vs the requirements of the US
National Electric Code (NEC).
 
Background:  A high tech piece of laboratory equipment about the size of a
dishwasher, designed and tested to the safety requirements of the
UL/IEC/EN 61010-1 (currently not NRTL listed).  Within this instrument we
have several linear power supplies each fed by a step down transformer
about the size of you fist (or smaller).  These transformers step down
230VAC 50/60hz to 24V, 12V, 5V, 3.3V (you get the idea).  These
transformers are panel mounted separate from the rest of the power supply
circuit for ease of assembly and to improve cooling and air flow. The
instrument has a 9 amp circuit breaker on the Mains. 
 
Because the primary current on these transformers are so low (in some
cases 0.01 amp), we use secondary fuses to protect the transformers from
overheating during the secondary Overload and Short-Circuit fault tests
according to the 61010-1 standard.  The 61010-1 standard does not dictate
how to protect the transformer, only that is must be done.  (generally we
use a primary fuse, or a secondary fuse, or both, or a thermally protected
transformer). 
 
However....
 
On occasion our instruments get inspected at the Customer Site to the
requirements of the NEC. This is either done by the local electrical
inspector or the company will hire an inspector to satisfy their insurance
company and/or OSHA inspector.  
 
Whatever the case, these inspectors will sometimes say that Article 450 of
the NEC requires a primary over-current protection device on ALL
transformers. In our case, they say that the requirements of Table
450-3(b) apply where we have to have a primary fuse no larger than 250% of
the primary current.  Finding a 0.05 amp fuse is not easy and we fear that
the inrush current on these transformers will fault trip such a small fuse
value.
 
When I argue that such a primary fuse would not protect the transformer
they say, "I'm only going by the letter of the law", or something like
that.  
 
When I ask if Exception No. 2: applies (Dry-type transformers that
constitute a component part of other apparatus and comply with the
requirements for such apparatus.)  they say NO because the transformers
are not mounted as part of the linear power supply circuit.
 
So (finally getting to the question), do I really need to have a primary
over-current protection device on every transformer regardless if it
serves any purpose or not?  OR should the NEC requirements not apply to
such an application?  
 
A little more info:  The transformer primaries are current limited by a 9
amp circuit breaker in a branch circuit. The wiring can handle this
current so a primary fuse is not needed to protect the conductors.
 
Thanks to all.
The Other Brian

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to