A device intended for the EU consists of a digital controller and resistive
heating elements in an enclosure, single phase device.

The digital controller draws 1A (give or take for sake of discussion) and
controls a contactor that opens and closes the power on the heater and
displays system info on an LED display.  The only ports are the AC mains and
a water inlet similar to a refrigerator water line.  The heater draws 42A
when connected.  This device is intended to be in the back room of retail
establishments and meets the safety requirements of 600335-2-85. 

 

The question, which EMC standard applies?  

 

55014 excludes from its scope “regulating controls and equipment with
regulating controls incorporating semiconductor

devices with a rated input current of more than 25 A per phase”.  Would
this constitute a regulating control?

 

61000-3-2 and 61000-3-3 are for devices under 16A, which the controller most
definitely is such a device, but the complete product is not.

 

My best judgment is the following:

 

EN61000-6-1, Immunity tests called out therein:

61000-4-2, ESD

61000-4-3, Radiated RF fields

61000-4-4, electrical fast transients

61000-4-5, surge

61000-4-6, conducted RF signals

61000-4-11, voltage dips and interrupts (which doesn’t apply for devices
over 16A, see above regarding 61000-3-2)

EN61000-6-3, Emissions tests called out therein:

61000-3-11, Limitation of voltage changes, voltage fluctuations and flicker in
public low-voltage supply systems - Equipment with rated current ≤ 75 A and
subject to conditional connection

61000-3-12, Limits for harmonic currents produced by equipment connected to
public low-voltage systems with input current > 16 A and ≤ 75 A per phase

                CISPR 16-2-3, radiated emissions (30MHz-1GHz)

                CISPR 16-2-1, conducted emissions (150kHz-30MHz)

 

That seems rationale to me, but I was still asked the question: 

Would it be appropriate to test the device with the heater disconnected and
treat it as a product only drawing 1A?

 

Thoughts/opinions welcomed.  Please correct me if I am befuddled, serves me
right for answering the phone at 5PM on a Friday.

 

Thanks,

Doug Kramer

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to