Apologies if this is duplicated, but I don't think it made it through went I
sent it yesterday. 

Tim, 
as you are based in the UK, this might be of some interest. 

According to 523.7 of BS 7671:2008 (commonly referred to as the "Wiring
Regs")....... 

where a cable is totally surrounded by thermal insulation having a greater
thermal conductivity than 0.04 Wm-1K-1, the following derating factors are
applied: 

length in insulation(mm)                Derating factor 
50                                0.88 
100                                0.78 
200                                0.63 
400                                0.51 
500 or more                        0.50 

These apply for conductor sizes up to 10mm^2 and are applied to the tabulated
value for installation clipped direct to a surface (Reference method C). 
These are for UK electrical installations and  so are not directly relevant to
the original posting, but do give some insight into your question. 
Andy 


Best Regards,

Andrew Wood MInstP 
Engineer - Special Products 


  
LAND Instruments International 
Stubley Lane, Dronfield, Derbyshire
S18 1DJ, England



This e-mail and its contents may be confidential, privileged and protected by
law. Access is only authorised by the intended recipient. The contents of this
e-mail may not be disclosed to, or used by, anyone other than the intended
recipient, or stored or copied in any medium. If you are not the intended
recipient, please advise the sender immediately.

Land Instruments International is registered in London (Reg. No. 1659383)

Registered office: Land Instruments International Limited, 2 New Star Road, PO
Box 36, Leicester, Leicestershire, LE4 9JQ 



"Haynes, Tim (SELEX GALILEO, UK)" <[email protected]> 
Sent by: [email protected] 

03/02/2009 09:27 AM To
"Kunde, Brian" <[email protected]>, <[email protected]> 
cc
Subject
RE: De-Rating Hookup Wire

        




Hi, 
  
Do you also need to de-rate the section of wire that is thermally insulated by
the cable tie? Maybe the cable tie is too narrow to be of concern – but then
what width is needed before de-rating does become necessary? 
  
I agree – all de-rating factors need to be applied. 
  
Regards 
Tim 
  
************************ 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<[email protected]>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]> 

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]> 


Reply via email to