We are now required to perform IEC 61000-4-16 (Conducted Common Mode 
Disturbances), 10 kHz to 150 kHz, on our products (protective relays for 
electrical system control). One of the specifications for the test is that 
the total harmonic distortion (THD) of the applied disturbance signal 
needs to be below 1%. My question is what definition of THD did the 
committee have in mind when they put together the standard?

When I look around on IEC's web site http://www.electropedia.org/ I find 
this:

IEV ref 551-17-06: the ratio of the rms value of the harmonic content of 
an alternating quantity to the rms value of the fundamental component of 
the quantity 
IEV ref 702-07-62: the total harmonic factor at the output of a 
transmission channel or two port device producing harmonic distortion, 
when the input signal is a sinusoidal oscillation of specified frequency 
and amplitude
IEV ref 103-07-32: ratio of the rms value of the harmonic content of an 
alternating quantity to the rms value of the quantity

What this all comes down to for IEC 61000-4-16 is that the rms value of 
the harmonics must be below 0.01 (-40 dB) of the fundamental (give or take 
a smidge, depending on whether the harmonics are compared to the 
fundamental alone or the total signal. In practical terms, the ratios are 
the same at this distortion level).

My comment (and thus question): 1. This low level of harmonics is 
unnecessarily strict. 2. The effect on level of the disturbance signal is 
minimal even with total harmonic power at -20 dB relative to the 
fundamental. 3. It can be difficult to achieve -40 dB with broadband RF 
signal generators and power amplifiers. 4. Harmonics as high as -6 dBc are 
allowed for IEC 61000-4-3 radiated immunity. 5. Harmonics as high as -15 
dBc are allowed for IEC 61000-3-6 conducted immunity (which starts at 150 
kHz, exactly where IEC 61000-4-16 stops).

 I am wondering if the IEC committee really intended this, or if they were 
thinking of total harmonic distortion as a ratio of powers, as some 
definitions hold it to be. This would put the total harmonic power at -20 
dB relative to the fundamental, which is within the performance 
specifications of standard broadband RF equipment.

Donald Borowski
EMC Engineer
Schweitzer Engineering Labs
Pullman, WA, USA

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to