Hello Brian,

The likely clause is NFPA 70 210.8(B)(6). This clause requires GFCI protection 
in indoor wet locations for buildings that are not dwelling units. It is likely 
that the AHJ is applying their own interpretation to this clause to require a 
GFCI for equipment with a fixed water connection. The concern of the NEC is 
that if equipment has a faulty ground connection, a nearby sink other water 
source could provide an alternate ground return path. A person could touch both 
the equipment and the sink completing the loop. However, this doesn't make as 
much sense for equipment with a fixed water connection. You might be able to 
convince the AHJ that there isn't an alternate ground close by even with the 
water connection. If you require a copper water line, that may convince the AHJ 
that the equipment has a reliable alternate ground.

EMI may not be the issue causing GFCIs to trip. I've run into this problem when 
using electronically speed controlled motors. Leakage current for safety is 
measured using the human body model, which measures AC current in the 50 - 60 
Hz range. The circuit of IEC 60990 Figure 4 has a low pass filter formed by R1 
and C1. Equipment may have higher frequency leakage current that is blocked by 
the test circuit but is high enough to trip a GFCI. I once had an air 
conditioner with an electronically speed controlled motor. A standard meter 
read a leakage current of 9 mA while the IEC 60990 Figure 4 circuit read about 
2 mA. The equipment was safe, since the higher frequency currents were too high 
of frequency to interfere with the human heart rhythms. (The IEC 60990 circuit 
is designed to detect only the current that is harmful to people.) However, the 
GFCI looks at current of any frequency. If the problem is high-frequency 
leakage current, additional EMI suppression may not help.

One option is to consider a locking plug for your product. If you supply your 
product with a NEMA L6-20 for example, it won't plug into a standard outlet. 
The NEC has a number of exemptions for equipment plugged into a circuit with a 
single outlet or to industrial locking outlets. The AHJ may consider the outlet 
as providing a reliable ground connection if it is a purpose installed outlet 
not serving any other equipment. Consult with the AHJ to see if there are 
conditions under which the GFCI will not be required.

Ted Eckert
Compliance Engineer
Microsoft Corporation
[email protected]<mailto:[email protected]>

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: Bob Johnson [mailto:[email protected]]
Sent: Friday, April 13, 2012 8:34 PM
To: [email protected]
Subject: Re: GFCI for 230VAC Products


You need to determine more carefully what requirements must be met. There are 
two different ground fault concerns in the code. Ground Fault Circuit 
Interrupters (GFCIs) are used for protection of personnel from electrical shock 
and are needed in wet areas. Ground fault protection of equipment is required 
for motor circuits but this protection is for the wiring and motor, not 
protection against electric shock. GFCIs are not necessarily required simply by 
the presence of plumbing.

GFCIs are for protection of personnel from electric shock due to wet 
conditions. GFCI protection is generally required for receptacles due to the 
poor dependability of portable circuits and grounding. Only in some areas like 
pools are additional permanently installed equipments required to provide 
protection from shock.

The NEC (NFPA 70-2012) requires GFCIs in the locations below. The code in 
effect is the one adopted by Tennessee which may be this or an earlier version 
of NFPA 70 and may have modifications.

The GFCI and/or motor ground fault protection is usually part of the site 
installation done by the local electrician. That generally makes it a burden on 
the owner, not the product manufacturer unless the product codes require it to 
be built in. Which GFCI or motor protectors to choose would often depend on the 
brand of electrical panel involved.

The following locations require GFCIs to some extent. There are exceptions and 
limitations. Sometimes 120V receptacles are required. Sometimes circuits must 
be protected.
Bathrooms
Garages
Crawl spaces
Unfinished Basements
Kitchens
Sinks
Boathouses
Boat Hoists
Indoor wet locations
Showers
Garages
Rooftops
Outdoors
Drinking Fountains
Spray Washers
Vending Machines
Hydromassage Units
Pools, Spas, Hot Tubs
Fountains
Marinas
Bodies of Water
Electric Signs
Electrified parking spaces
Elevators and lifts
Space Heating Cables
Construction Sites -
Health Care Facilities
Mobile Homes
Recreational Vehicles
Pipeline Heating
Aircraft Hangers

Bob Johnson
ITE Safety<www.itesafety.com>



On 04/13/2012 10:22 AM, Kunde, Brian wrote:
Our company makes a 230VAC product (laboratory/light industrial) that has a 
water connection. We received word from a customer in Tennessee, USA, who says 
the NEC and/or the Tennessee Electric Code requires a GFCI be used with this 
product. We are not experts in the NEC so can anyone confirm this to be true? 
We did not know GFCI were required for non-consumer products.

Our product uses a Frequency Drive to speed control a 2hp motor. EMI from the 
drive causes false trips in the GFCI.  On a similar 115VAC product we found 
GFCI based on the 2006 requirements worked just fine as was immune to the EMI 
caused by a Frequency Drive, but we cannot find such a reference on 230VAC GFCI.

Can anyone suggest a 230VAC 2 pole GFCI that is immune to EMI from Frequency 
Drives?

Does the NEC allow for an alternative for a GFCI such as adding a secondary 
earthed ground bonding conductor or wiring the power cord direct?

Thank you all for your help.

The Other Brian


________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to