The 2008 National Electrical Code (NFPA 70) added a requirement for tamper 
resistant receptacles. Article 210.52 covers "dwelling unit receptacles" and 
specifies general provisions for outlets used in residential installations. 
Article 406.11 is a new section that specifies that all 125 V, 15 or 20 A 
receptacles covered under 210.52 must be tamper resistant.
http://www.nfpa.org/assets/files//PDF/Fact%20sheets/TamperResistant.pdf<http://www.nfpa.org/assets/files/PDF/Fact%20sheets/TamperResistant.pdf>

The result has been that ground fault circuit interrupters (GFCIs) have been 
introduced with shutters. However, all of the major manufacturers that I 
reviewed only have the shutters on line and neutral. The shutters open only 
when plug blades are inserted in both openings simultaneously. The intention is 
to prevent young children from getting a shock by inserting a foreign object 
into the outlet.

The National Electrical Code (NEC) does not require GFCIs to have a ground 
connection. In fact, the NEC specifies that GFCIs be used for protection is 
certain situations where no grounding conductor is available. (See NEC article 
406(D)(3).) GFCIs are required in kitchens near sources of water, and most 
kitchen appliances are double-insulated without a ground pin. The same is true 
for many items plugged into bathroom outlets, such as electric razors and 
electric toothbrush charging bases. A GFCI requiring a three-prong plug would 
likely pose a problem in these areas.

I would be a bit suspicious of GFCI receptacles that require the insertion of a 
grounded plug. I can imagine a scenario where somebody determined that it would 
be acceptable to force people to use grounded plugs instead of providing GFCIs. 
Did the builder consider having a wired path to earth sufficient to meet the 
intent of the GFCI requirements? I recommend pulling the cover plate for one of 
the outlets to try to find the manufacturer's name and part number. Look up the 
specifications on the outlet to see if is even a GFCI. Also, if this is a UL 
Listed tamper resistant outlet, the words "Tamper Resistant" or the letters 
"TR" must be visible on the device even with the cover plate installed and at 
least 4.8 mm high. (See UL 498 Table 164.4, Reference 15.)

Note 1: The addition of the tamper resistant receptacle requirement along with 
the new Arc Fault Circuit Interrupter (AFCI) requirement have caused concern 
due to the increased cost and perceived reliability issues. A number of states 
and jurisdictions have not adopted either the 2008 or 2011 codes, or have 
adopted the codes while striking out these two requirements. It is possible 
that the tamper resistant requirement doesn't exist where you live and that 
this outlet was used for some other reason.

Note 2: AFCIs are relatively expensive. Shuttered GFCIs are not too expensive, 
but still cost more to make than a standard outlet. There has been a 
proliferation of counterfeit electrical devices including receptacles in the 
past decade. The counterfeiters will copy the manufacturer's marking and even 
the UL mark but there are usually ways to see if the outlet is fake.

Ted Eckert
Compliance Engineer
Microsoft Corporation
[email protected]<mailto:[email protected]>

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: Ken Javor [mailto:[email protected]]
Sent: Friday, June 29, 2012 7:31 PM
To: [email protected]
Subject: New type of GFI?

All,

In a brand new building in the USA using a type of GFI in wet areas 
(kitchen/bath) with which I am unfamiliar.  These GFIs require a three prong 
plug in order to be able to insert. The ground pin pushes back a plastic 
blocking sheath which otherwise blocks the insertion of any two prong plug.

Question:  Does this type of GFI require a three prong device in order for the 
device to be able to detect a fault condition (i.e., does it only sense current 
in the safety wire conductor, or is it some sort of belts and suspenders design 
that works like GFIs which accept two wire plugs)?

Another way to phrase the question is whether or not it is safe to plug in a 
two prong device using a cheater plug.  For example, a DEI (doubly electrically 
isolated) electric razor with a two prong plug cannot be plugged into the 
electrical outlet near the bathroom sink without the cheater plug.

Not looking for a sermon on safety here, just a definitive answer on the design 
of this type of GFI, and the impact of using the cheater.  Common sense would 
indicate that this new device would have to work the same as older devices else 
people using cheaters to bypass them would be incurring a risk that didn't use 
to exist with previous generations of GFI.  Wishing to confirm that.

Thank you,

Ken Javor
Phone: (256) 650-5261
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to