Dear all,

Please check below link. I must say I do not agree with last paragraph on page 
7, since they do not consider internally generated high voltages. Even the 
input is SELV, internally there might he high voltages generated and therefore 
by having only functional insulation in-out, fault conditions are required in 
order to verify that output remains SELV.


http://archive.ericsson.net/service/internet/picov/get?DocNo=31/28701-FGB101378&Lang=EN&HighestFree=Y



Boštjan Glavič









On 20. jan. 2015, at 20:05, "Scott Aldous" 
<[email protected]<mailto:[email protected]>>
 wrote:

For the power supplies that are certified by UL under category code QQGQ2, UL 
does have a standardized table format on their online cert directory that 
includes a code they call the Output Category. The intent is to identify those 
supplies that have been evaluated for SELV output, or other types of output. 
More information can be found in the guide card for that category:

http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=QQGQ2.GuideInfo&ccnshorttitle=Power+Supplies,+Information+Technology+Equipment+Including+Electrical+Business+Equipment+-+Component&objid=1073787375&cfgid=1073741824&version=versionless&parent_id=1073787374&sequence=1

On Tue, Jan 20, 2015 at 10:17 AM, Brian Oconnell 
<[email protected]<mailto:[email protected]>> wrote:

Mr. Nute’s response is significant and is worthy of re-emphasis.



And Mr. Woodgate answered this same question to Mr. Nyffenegger previously:



" The power supply as a whole cannot claim that unless ALL its outputs

meet the SELV requirements. But it does meet the requirements for safety

isolation, so those outputs that meet the voltage requirements are SELV."



SELV, TNVx, LPS, LCC, etc are specific ratings that would be indicated in the 
Conditions of Acceptability in both the test certification document required to 
bear a CAB’s logo and the respective CB report. And as many power supplies are 
components, the report will be necessarily incomplete; and only the assessment 
in the end-use construction can provide a complete report.



Per Mr. Nute, other than simple flyback converters, most component SMPS are too 
complex to be evaluated by other than an assessment directed by the original 
manufacturer (in last 15 years, have encountered only three agency engineers 
capable of a complete and independent assessment of SMPS). There is never any 
logical reason to assume a ‘certified’ component power supply will meet any 
specific ratings unless stated in a CAB’s report.



Brian



-----Original Message-----
From: Richard Nute [mailto:[email protected]<mailto:[email protected]>]
Sent: Monday, January 19, 2015 12:55 PM
To: [email protected]<mailto:[email protected]>
Subject: Re: [PSES] SELV rated power supplies



Hi Dave:



EN60950-1 is not equal to SELV.



Certifications and reports do not necessarily

indicate outputs are SELV, although careful

reading of the test results can conclude that the

outputs are SELV or not.



Not all outputs of EN60950-1 power supplies are

SELV and need not be.  The power supplies are

nevertheless EN60950-1 power supplies.



The requirement for SELV is whether or not the

circuit is accessible.  Accessible circuits must

be SELV.



To perform a single-fault test, one must

understand how the circuits operate, and what

faults could cause the output to possibly exceed

SELV limits.  In today's power supply topology,

such circuit analysis is not necessarily

straight-forward.



Your statement



"Therefore my contention is it cannot be assumed

that a power supply listed as EN 60950-1 compliant

on a manufacturer's data sheet is also SELV

compliant unless explicitly stated so or proven in

the test report results."



is correct.



Best regards,

Rich

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;[email protected]<mailto:[email protected]>&GT;

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas &LT;[email protected]<mailto:[email protected]>&GT;
Mike Cantwell &LT;[email protected]<mailto:[email protected]>&GT;

For policy questions, send mail to:
Jim Bacher &LT;[email protected]<mailto:[email protected]>&GT;
David Heald &LT;[email protected]<mailto:[email protected]>&GT;



--
Scott Aldous
Compliance Engineer
Google
650-253-1994
[email protected]<mailto:[email protected]>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to