Robert,

Your fuses should not blow, and we always test 5 positive and 5 negative at 0º, 
90º, 180º and 270º. We also test at lower voltage levels, starting at 500V, the 
increasing to 1kV, 2kV, 3kV, and so on. By the time you get to 8kV your circuit 
would have been hit hundreds of time. You can probably change out your circuit 
as a point where you think your MOVs have served out its usefulness. But we 
have tested such circuits under thousands of hits without the MOVs failing, so 
just be aware. When the MOVs fail short, your overcurrent protection device 
will normally trip because once the Gas Tubes conduct they won't let go once 
the MOVs short.

The Other Brian

From: Rob Oglesbee [mailto:[email protected]]
Sent: Tuesday, August 04, 2015 3:23 PM
To: [email protected]
Subject: [PSES] IEC 61010-2-030 Transient Overvoltage Testing

I have a circuit I'm using to reduce the Overvoltage Category Level from 
600V/CAT IV to 600V/CAT II before hitting an instrumentation transformer.  I 
wish to test it per IEC 61010-2-030 Clause 14.101 (Circuits or components used 
as Transient Overvoltage limiting devices in measuring circuits used to measure 
Mains).  The requirement is 5 positive and 5 negative impulses from a hybrid 
impulse generator at 8000V (1.2/50us O.C., 8/20us S.C., 2 ohms) while Mains is 
applied.  Up to a minute is allowed between impulses.  The pass criteria for 
the test is that no Hazard shall arise, and that the Mains breaker is not 
tripped.

My circuit is a combination of MOVs and GDTs with fast fusing on both input 
legs.  On the first impulse the protection circuitry will blow the fuses.  My 
first question is, do I replace fuses between impulses (I think not)?  My 
second question is, what phase angle should I perform the test at (I think 
worst case, +90 for positive and +270 for negative)?

Thanks,
Robert A. Oglesbee
Radian Research, Inc.
(765) 449-5505

This message, and any attachments to it, may contain information that is 
privileged, confidential, and exempt from disclosure under applicable law. If 
the reader of this message is not the intended recipient, you are notified that 
any use, dissemination, distribution, copying, or communication of this message 
is strictly prohibited. If you have received this message in error, please 
notify the sender immediately by return e-mail or call 765-449-5500 and delete 
the message and any attachments. Thank you.

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to