On 26-Oct-15 6:29 PM, Scott Aldous wrote:
_Table 5 (Capacitor Energy)_

For the energy from a capacitor, the table takes into account capacitance and voltage, so both need to be taken into account since the equation for available energy from a capacitor includes both variables. This is similar to 2.1.1.5c)2) from 60950-1.

IEC 60479-2 provides a linearised treatment of a capacitive discharge to the body. The examples consider both capacitive discharge charge and energy. In TC108 safety documents IEC 60950-21 and the coming IEC 62368-3 you will find voltage versus maximum capacitance figures. What is counter-intuitive is that these curves are set by the capacitor charge. If you calculate the capacitor value from the maximum body energy value far greater values of capacitance result. Whoever calculated the figure capacitance values back in 2000 or so worked out that for Remote Feeding Telecommunication circuits the capacitive charge was the critical parameter, not energy, setting the maximum capacitance value.
Regards
Mick

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to