The LISNMARK (LISN MATE) is exactly the same device as what I linked to.

As for the current probes, comparing L and N to determine if one of cm or dm 
predominates... we are talking about noise signals, and measuring magnitudes 
(no phase info) in frequency domain, right? I know that on one conductor, you 
can say CM/DM add while they subtract on the other (mathematically correct no 
matter which you call L and which you call N). I'm confused at how you know it 
cannot be similar amounts CM and DM noise when the noise magnitude is the same 
between L and N. I'd appreciate it if you could explain.

Obviously running L+N simultaneously through the same probe gives common-mode 
noise, I'm not sure if I worded my response badly because I meant to say bullet 
#3 is completely correct (as is 1, along with 4 assuming no "LISNMATE")

Elliott Martinson
Product Assurance Specialist I
Electronic Theatre Controls
3031 N PLEASANT VIEW RD
MIDDLETON WI 53562-4809
Work: 608.824.5696 / Cell: 608.209.9897
[email protected]

From: Ken Javor [mailto:[email protected]]
Sent: Tuesday, March 29, 2016 4:14 PM
To: [email protected]
Subject: Re: [PSES] Commom mode current vs. differential mode current and LISN

Disagree. Westin had it right. A current probe can be used to isolate either cm 
or dm current. If at any frequency the signal amplitude on individual line and 
neutral conductors are very close, then all you can say is that at that 
frequency either cm or dm predominates, but you can't say which.  With a LISN, 
a separate device must be used. Mark Nave of EMC Services designed a three port 
device (connects to each LISN port and to the EMI receiver) trademarked 
LISNMATE in the 1980s to isolate common mode, and sometime later he produced 
LISNMARK, which isolated DM.  Within the past decade, Ray Adams while at 
Fischer Custom Communications packed both functions in one piece of equipment, 
which if memory serves was named LISNUP.

EMC Services, Mark Nave's company, is no longer producing his products, but I 
believe the FCC product is still available.

Ken Javor
Ph. (256) 650-5261


________________________________
From: Elliott Martinson 
<[email protected]<mailto:[email protected]>>
Reply-To: Elliott Martinson 
<[email protected]<mailto:[email protected]>>
Date: Tue, 29 Mar 2016 20:36:18 +0000
To: <[email protected]<mailto:[email protected]>>
Conversation: [PSES] Commom mode current vs. differential mode current and LISN
Subject: Re: [PSES] Commom mode current vs. differential mode current and LISN

http://www.hottconsultants.com/techtips/CM_vs_DM%20Conducted_Emission.html
This is a great resource for your question.

Your second point kind of contradicts your first, if it's trying to say what I 
think it is. DM and CM each show up on L, but the same is true for N. It's a 
linear combination of both, so even if L and N are almost equal, you can't say 
anything about the proportion of DM to CM currents.

If they are not equal, then this implies current is travelling back via the 
ground conductor and/or energy's being lost to radiated emissions.

What you need is a physical circuit to do the adding/subtracting of the LISN 
outputs. (otherwise your 3rd bullet point is correct)

Your 4th bullet, well I refer you to the link above.


Elliott Martinson
Product Assurance Specialist I
Electronic Theatre Controls
3031 N PLEASANT VIEW RD
MIDDLETON WI 53562-4809
Work: 608.824.5696 / Cell: 608.209.9897
[email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>


From: Amund Westin [mailto:[email protected]]
Sent: Tuesday, March 29, 2016 1:23 PM
To: [email protected]<mailto:[email protected]>
Subject: [PSES] Commom mode current vs. differential mode current and LISN

Please correct me, if I am wrong (that happens quite often ...):

*        Let one wire (L) pass through a current clamp, and you measure the 
combination of current mode and differential mode currents

*        Do the same with wire N. If L and N are (almost) equal, you either 
have major part of DM currents or major part of CM current

*        Let both wire (L and N) pass through a current clamp, and you measure 
the only CM current (DM is canceled)

*         When doing conducted emission test by LISN, you actually get what you 
get. LISN do not see the difference between CM or DM. From LISN measurements, 
you can't say if noise is CM or DM.

B.regards

Amund













-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html><http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:      http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) 
<http://www.ieee-pses.org/list.html><http://www.ieee-pses.org/list.html>
List rules:     http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher  <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]<mailto:[email protected]>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]<mailto:[email protected]>>
Mike Cantwell <[email protected]<mailto:[email protected]>>

For policy questions, send mail to:
Jim Bacher <[email protected]<mailto:[email protected]>>
David Heald <[email protected]<mailto:[email protected]>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to