Hi Ken,

With short delay, Thank you.

So on short, if flexible cord is used, cord must have a plug, if wiring 
terminals are used, cord must be put in conduits.

Do you know the background of this requirement? Is this applicable even if unit 
is used in a computer room with raised floor?

Best regards,
Bostjan

From: IBM Ken [mailto:ibm...@gmail.com]
Sent: Monday, September 5, 2016 6:52 PM
To: Boštjan Glavič <bostjan.gla...@siq.si>
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Connection to ac mains with split end line cord

Hi Bostjan!

NEC (NFPA 70) has an Article 645 which covers "Information technology 
equipment" rooms.  This article states, among other things, that flexible 
linecords must have a 'plug cap'.
People sometimes mistakenly stop their analysis there, stating either that the 
intended installation location is not an "ITE room" or that the local Authority 
Having Jurisdisction has waived that requirement.

However, 60950-1 has D1 deviations and Annex NAE makes specific reference to 
the fact that equipment must comply with the requirements in article 645 of 
NFPA 70.  Therefore, ITE (regardless of what the intended installation location 
is or what the AHJ says) Listed to 60950 must comply by having a plug on the 
end of the flexible line cord (which also must be <14' long after exiting the 
cabinet, by the way).

Some will attempt to work around this by declaring the mains branch circuit 
breaker box as another piece of ITE and then declaring the flexible linecord as 
'interconnecting cable' but this is not legitimate either.

The only accepted method of providing stripped power leads that meets the 
requirements of 60950-1 and the NEC is to provide the equipment with wiring 
terminals and provision for mounting of conduit.

-Ken A

On Mon, Sep 5, 2016 at 9:36 AM, Boštjan Glavič 
<bostjan.gla...@siq.si<mailto:bostjan.gla...@siq.si>> wrote:
Dear experts,

Can you help me with below item. I do not have experiences with NEC/CEC. Some 
people told me that only ATMs are allowed to be connected to mains without the 
plug, but i think this is strange requirement.

Customer has an IT equipment cabinet (IEC 60950-1) with built-in power supply 
rack (shelf) with several modular power supplies. Power of such cabinet is 
rated round 200 kVA. The power supply rack is provided with two special (UL 
1977) input connectors. Connection to supply will be realized by split end line 
cord (with plug/connector on unit side and split end on the other side). Split 
end of the cord will be connected to junction box mounted under the floor. 
Junction box will be connected to control panel. Unit will not be directly 
supplied from the panel, but always from the junction box.
Cables and connectors will not be visible / accessible from outside, but only 
after opening of front cover of the end system rack (this action is allowed to 
service personnel only).

Manual circuit breaker will be provided in wall installation.

Is such construction acceptable by NEC and CEC?

Best regards,
Bostjan

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald: <dhe...@gmail.com<mailto:dhe...@gmail.com>>


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to