Ralph, et al,

        My long term understanding is that the fault current is a curve.  High 
values initially draining to lower values as the stored charge in the adjacent 
wiring is pulled thru the short circuit and maintained by the supply impedance 
at the longer term value.  

        According to what UL has told us for years, the peak SS current from a 
usual commercial or  residential 120V outlet on a 15A or 20A circuit is 7000 A 
peak (probably for microseconds).  

        I have seen SS tests done on equipment used on 600V industrial circuits 
where a 10,000 A clearing capacity was tested.  

        The failure in misapplication results in ionization of the gas in the 
fuse along with the metallic residue from the interrupted fuse which continues 
to conduct until some other component open (hopefully before the conflagration 
is fully underway).  

        Europeans claim a lower SS current from their systems (higher 
impedance, it seems); so the fuses used there have lower clearing capacity.  

:>)     br,      Pete

Peter E Perkins, PE
Principal Product Safety & Regulatory Affairs Consultant
PO Box 23427
Tigard, ORe  97281-3427

503/452-1201

p.perk...@ieee.org

-----Original Message-----
From: Ralph McDiarmid [mailto:ralph.mcdiar...@schneider-electric.com] 
Sent: Monday, November 20, 2017 10:42 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?

According to IEC/TR 60725, 90% of customers in the UK and in Australia, will 
have electricity supply impedance less than or equal to 0.25 + j0.23 ohms.  
That according to a survey or residential service for 230V/50Hz

That tells me that short circuit current would be at least 680A, but could be 
twice that value or higher for some customers

Ralph McDiarmid
Product Compliance
Engineering
Solar Business
Schneider Electric


-----Original Message-----
From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Monday, November 20, 2017 10:26 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?

Mr. Woodgate,

Is there a recently published spec for a 'typical' 230V mains impedance for the 
EU? Have also noted that the source Zs in 61000-4-5 for the instrument seem 
rather high. So what is the basis for 1500A interrupt rating?

For U.S., even for an artificially low-Z electronic AC source, seldom see fault 
currents exceed 200A peak for 120V mains. Conversely, have noted that at over 
100A fault current, any fuse not rated for the 'high' interrupt value will 
probably explode.

So either our ratings are suspect, or perhaps the physics behind the standards 
are not complete?

Brian



From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Friday, November 17, 2017 11:16 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?

I'm afraid that's not so. The short-circuit current of a 20 A circuit is 
normally at least 500 A, maybe 1500 A.
John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2017-11-18 
03:49, Joe Randolph wrote:
Yes, that is a very good point.  I may have misinterpreted what the term 
“adequate breaking capacity” means.  If all it means is that the fuse must be 
able to safely break the short-circuit current, then a 20 Amp, 250 VRMS fuse 
would be fine for use on a 20 Amp, 240 VRMS circuit.
 
Of course, this would not provide much protection against overheating of the 
MOV unless the MOV failed at an effective resistance of less than 12 ohms.  
Anything higher than that would just keep producing heat.
 
Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.com
 
From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Friday, November 17, 2017 4:47 PM
To: Joe Randolph <j...@randolph-telecom.com>; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?
 
I agree with this step-wise route to failure. But I wonder about the intended 
meaning of 'adequate breaking capacity'. In the context of the fuse standard 
IEC 60027 (multi-part), this means that the fuse must not shatter or arc-over 
with the largest fault current that can be applied to it. It's all about the 
fuse, not about what it is supposed to protect. 
I believe TVSs (BIG diodes with integral heat sink) are much nicer devices to 
use than MOVs. They don't suffer from energetic disruption.
John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2017-11-17 
21:39, Joe Randolph wrote:
I have not performed any actual testing, but I believe that the basic problem 
is that MOV leakage current increases slightly each time the MOV experiences a 
big surge.  So, in the early stages of this mechanism, the leakage current will 
increase step-wise each time the MOV experiences a big surge.
 
In practice, these successive "big surges" could be spaced months or years 
apart.  Each successive surge will increase the leakage current, but if the 
current remains well below the level that causes significant self-heating of 
the MOV, the situation will remain stable.
 
After some number of big surges (which could take years to accumulate), the 
leakage current will have increased enough that the self-heating process itself 
leads to higher leakage current.  This sets up a positive feedback loop that 
causes the MOV to go into thermal runaway and self-destruct.
 
I'm not sure the thermal runaway could be described as an "avalanche," since 
the process might take considerable time to destroy the MOV, but the general 
direction of the failure gets establishes as soon as the positive feedback 
mechanism gets started.  
 
If it could be shown that any dissipation level less than 240 W cannot cause 
ignition of nearby materials, then a 1A fuse would appear to provide the 
"adequate breaking capacity" called for in 60950-1.
 
Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.com
 
 
-----Original Message-----
From: Ralph McDiarmid [mailto:ralph.mcdiar...@schneider-electric.com]
Sent: Friday, November 17, 2017 1:05 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?
 
I wonder if a 1A fuse would protect against MOV flameout just as well as a 
100mA, if these MOV fail as an avalanche.  (get hotter = more leakage) I've 
seen some standards use 240VA (assume 240W) as a power limit for protection 
against fire.  However, I wonder if a MOV could burn nicely at say 0.5A without 
further increase in current.
 
Ralph McDiarmid
Product Compliance
Engineering
Solar Business
Schneider Electric
 
 
-----Original Message-----
From: Joe Randolph [mailto:j...@randolph-telecom.com]
Sent: Monday, November 13, 2017 7:56 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?
 
Hi Mick:
 
Annex Q  in 60950-1 shows that the authors were concerned about increased 
leakage current in MOVs that are subjected to multiple surges.  Perhaps the 
authors assumed that if the equipment passed the earth leakage test with new 
MOVs, allowing the MOVs to deteriorate by up to 10% after the Annex Q surges 
would be acceptable.  
 
Unfortunately, Annex Q does not help to define the term "adequate breaking 
capacity" as called for in clause 1.5.9.2 for fuses required in series with the 
MOV.  As Rich Nute has pointed out, a fuse that will open when the leakage 
current exceeds 0.5 mA cannot be expected to survive a 3 kA surge.
 
So, the purpose of the fuse does not appear to be directed at the 0.5 mA 
leakage current requirement.  Rather, I think the authors were trying to use 
the fuse to protect against the three conditions itemized in clause 1.5.9.2:
 
* Temporary overvoltages
* Thermal overload due to increased leakage current
* Burning and bursting of the MOV in the event of a short-circuit fault
 
The problem with this is that it takes very little leakage current to cause 
thermal overload of the MOV.  At 230 VRMS, and RMS leakage current of 100 mA 
would dissipate 23 Watts in the MOV.  A fuse that reliably opens at 100 mA will 
not survive a 3 kA surge.  
 
In general, MOVs subjected to thermal overload allow more leakage current as 
they heat up.  With a fixed voltage supply (such as 230 VRMS), this creates a 
positive-feedback condition of ever-increasing power dissipation that 
eventually drives the MOV to destruction.
 
So, perhaps the requirement for "adequate breaking capacity" was directed at 
trying to prevent burning and busting of the MOV, rather than excessive earth 
leakage current.  So far, it appears that the term "adequate breaking capacity" 
is not actually defined in 60950-1.  I suppose that the authors intended 
"adequate breaking capacity" to mean "adequate to prevent burning and bursting" 
of the MOV.  
 
I'm not sure that this is even possible if that same fuse has to survive a 3 kA 
combination wave surge.  However, it is possible that 60950-1 does not actually 
require the circuit to survive such surges.  Perhaps all that 60950-1 requires 
is that the MOV itself tolerates such surges with no more than 10% degradation. 
 It would then be left to the product designer to select a suitable fuse.  
Between the conflicting goals of preventing nuisance tripping of the fuse and 
preventing overheating of the MOV, I'm not sure that an ordinary fuse can be 
found that meets both goals.
 
This may be why 62368-1 seems to be steering us to using a thermal fuse that 
senses overheating of the MOV, rather than a fuse that responds only to current.
 
 
Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848 (USA)
j...@randolph-telecom.com
http://www.randolph-telecom.com
 
 
-----Original Message-----
From: Mick Maytum [mailto:mjmay...@gmail.com]
Sent: Sunday, November 12, 2017 3:55 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on 
AC mains ports?
 
For my sins I am currently editing a 40 page MOV application guide. As the 
guide was written by a Chinese expert I have the additional task of translating 
the Chinlish to English. However this forces understanding and I found the 
document contains many gems I did not appreciate. On degradation three areas 
are mentioned:
 
1.       Varistor voltage at 1mA has decreased by more than 10 % of the initial 
value.
2.       Surge limiting voltage at a specified impulse current has increased by 
more than 10 % of the initial value.
3.       Leakage current or watt-loss shows a steady increase.
 
Then the comment is made that generally if the Varistor voltage has decreased 
by 10 %, the limiting voltage will have only increased by 3 %. 
Thus the Annex Q limiting voltage change limit of 10 % would be better replaced 
by a Varistor voltage change.
 
On fuses I did some calculations and found an anti-surge fuse in the 4 A region 
was required to withstand the Annex Q MOV requirement of a 3 kA
8/20 surge. It should be remembered that most fuses will not interrupt an 8/20 
surge as the fuse link plasma carries on conducing the 8/20 impulse current. 
Ted makes the excellent point that in the equipment additional series 
impedances will exist that reduce the peak the peak surge current from an 
1.2/50-8/20 generator.
Tests are now appearing for thermally protected MOVs, which disconnect the MOV 
in the event of exceeding a pre-set body temperature limit. 
Thermal disconnect, rather than current disconnect, gets to the heart of the 
matter. But, as far as I'm aware, none of these tests apply a surge voltage to 
check for open thermal switch arc over.
 
Regards,
 
Mick Maytum
Safety and Telecom
Standards
mjmay...@gmail.com
https://ictsp-essays.info
  

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)