See below.
John Woodgate OOO-Own Opinions Only
J M Woodgate and Associates www.woodjohn.uk
Rayleigh, Essex UK
On 2018-03-13 19:57, John Woodgate wrote:
I suspect that the SELV circuits of an electricity meter never leave
the enclosure, so SELV is OK, but PELV would still be equally safe or
better, even if a very low probability open-circuit earth occurred.
John Woodgate OOO-Own Opinions Only
J M Woodgate and Associateswww.woodjohn.uk
Rayleigh, Essex UK
On 2018-03-13 19:17, Ted Eckert wrote:
Part of the reason why two levels of protection are required is
because of what happens if one level fails. If the protective earth
bonding connection fails, and the exposed metal is no longer earthed,
the product will typically continue to operate normally. There is no
indication to the user that a failure has occurred. If a second
failure occurs that bridges the insulation gap between hazardous
voltage and that exposed metal, the chassis will become energized.
The user may still have no obvious indication of a failure until they
contact that energized chassis.
Different standards committees have different ways of addressing this
issue. TC 108 generally requires that the protective earth bonding be
designed and tested in such a way to prove that it is robust enough.
In many ITE products, the user accessible circuits are earth ground
references, so providing basic insulation between SELV and earth
ground is not possible. Other standards committees may have chosen
other methods of protection based on the products they cover. TC 13
may have decided that basic insulation between SELV and earthed parts
may be the best way to provide protection in their products. In this
case, if the earth bonding fails, the basic insulation may be need to
reduce the risk or arcing between hazardous voltage and the exposed
metal.
Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect
those of my employer, TC 13 or TC 108.
*From:* Scott Aldous <00000220f70c299a-dmarc-requ...@ieee.org
<mailto:00000220f70c299a-dmarc-requ...@ieee.org>>
*Sent:* Tuesday, March 13, 2018 8:57 AM
*To:* EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
*Subject:* Re: [PSES] insulation between SELV and protective earthed
accessible part- IEC 62052-31
Hi Vyas,
I'm not familiar with this standard, but the general principle is
that 2 levels of protection are required to protect operators from
hazards. In the case of the "protective earthed accessible part", I
imagine the standard assumes that a single fault could compromise the
protective earthing, so Basic or Supplementary Insulation is also
required between such a circuit and SELV. In the same vein, the table
requires Double or Reinforced Insulation between an "unearthed
accessible part" and SELV.
On Tue, Mar 13, 2018 at 5:56 AM, Balmukund Vyas
<balmukund.v...@ymllabs.com <mailto:balmukund.v...@ymllabs.com>> wrote:
Dear All,
IEC 62052-31 is standard for product safety requirements for
electricity metering equipment. It has a table 20 (given below)
which details out insulation requirements between various types
of circuits.
My question is, why Basic insulation is required between SELV
circuit and protective earthed accessible parts? Isn’t a
functional insulation is sufficient for this?
Thanks
B M Vyas
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to <emc-p...@ieee.org <mailto:emc-p...@ieee.org>>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities
site at http://product-compliance.oc.ieee.org/ can be used for
graphics (in well-used formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to
unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org>>
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com>>
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion
list. To post a message to the list, send your e-mail to <emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>
For policy questions, send mail to:
Jim Bacher: <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>