Depends on Security Grade requirements and where the battery is stored.

Li batteries can be used in discharge mode to -20C.  Have only done one project 
for this, where the battery temperature was monitored by the charger, and shut 
down charge current when outside rated temperature range, but allowed discharge 
to -20C.

Brian


From: Amund Westin [mailto:[email protected]] 
Sent: Monday, April 16, 2018 11:42 PM
To: [email protected]
Subject: [PSES] EN50131-1 Battery spec vs. Environmental class

EN50131-1: Alarm systems - Intrusion and hold-up systems -- Part 1: System 
requirements

>From the standard:
Environmental Class II: Indoor General (-10º to +40º)


Li-Ion batteries may have this spec:
Charging: 0º C to 45º C
Discharge/standby: -20ºC to +50º C:

As I understand the Li-Ion tech, the batteries should not be charged when 
temperature is below 0º C and that means it's not possible to qualify for 
Environmental Class II (-10º to +40º) Indoor General.
Unless you monitor the temperature and prevents charging when temperature is 
under 0º C, but that may lead you into other trouble if temperature remains low 
over a long period.
Any others who has considered the same case and agree?

Best regards
Amund 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to