Ken:

That "...some arcing/sparking along the way..." can be very dramatic. I 
wouldn't be surprised to examine such a conduit / ground path after a strike 
and find the bottom equipment box blown off the pole or maybe a foot or so of 
conduit has been vaporized and embedded in the pole.

Also, ground paths can be very long; envision a 1,500 foot high broadcast tower 
standing on the Nebraska plains. I wonder how many strikes the Petronas Towers 
endure in a year?

Ed Price
WB6WSN
Chula Vista, CA USA

From: Ken Javor [mailto:[email protected]]
Sent: Wednesday, May 15, 2019 10:06 AM
To: [email protected]
Subject: Re: [PSES] Just curiosity

If the purpose of the copper conductor is to act as a lightning rod, and ensure 
the lightning doesn't travel through the wood, does it matter if instead the 
conductor is galvanized pipe and there is some arcing/sparking along the way?

Ken Javor
Phone: (256) 650-5261

________________________________
From: Edward Price <[email protected]>
Reply-To: Edward Price <[email protected]>
Date: Wed, 15 May 2019 10:03:55 +0000
To: <[email protected]>
Conversation: Just curiosity
Subject: Re: [PSES] Just curiosity

Ken:

If a lightning path connects to the top of that conduit, what is the path to 
Earth ground for that charge? There are probably several screwed joints down 
the pole, and then, your photo shows the conduit running into an adapter (which 
itself looks to be clamped to the equipment box by an internal nut). And then, 
how is the box grounded? All those joints would be acceptable if they were 
welded, but chances are that each those joints has quite a bit more resistance 
than a welded joint. Perhaps some of those joints only have a few points of 
contact to effect the electrical connection. Dumping maybe 30 kA down that path 
could well result in some spectacular joint arcing.

I suspect that instead of going to the trouble of welding all the joints, the 
copper conductor provides the Earth bonding for a lot less cost.


Ed Price
WB6WSN
Chula Vista, CA USA



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to